York Modle #PBKM-LD20N120C lock out light


  #1  
Old 09-30-11, 07:46 PM
S
Member
Thread Starter
Join Date: Sep 2011
Location: usa
Posts: 2
Received 0 Votes on 0 Posts
Question York Modle #PBKM-LD20N120C lock out light

Just bought my house at the end of winter last year, and there was no problem with the furnace. Tryed to fire it up today to make sure it will work for this winter and nothing. When I open it up the light flashes once and does not turn back on. the tag said one flash means system lock out. When I open the bottom cover and push the button that tells it that the cover is in place, in a couple of times the blower starts for a second and then cuts out. Hope someone can help thanks for any advice you can give.
 
  #2  
Old 09-30-11, 08:06 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
a 1 flash would be repeated not flash once and then go out.
 
  #3  
Old 10-01-11, 07:05 AM
S
Member
Thread Starter
Join Date: Sep 2011
Location: usa
Posts: 2
Received 0 Votes on 0 Posts
So what would that mean, or does it mean that there is nothing wrong down there, and could it be my thermostat?
 
  #4  
Old 10-01-11, 03:21 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
remove the blower door, and tape the door switch closed next check for 24VAC between W and C with the stat calling for heat.
 
 