Older Whirlpool Gas Furnace Won't Come On


  #1  
Old 10-02-11, 09:35 AM
P
Member
Thread Starter
Join Date: Oct 2011
Location: us
Posts: 3
Received 0 Votes on 0 Posts
Older Whirlpool Gas Furnace Won't Come On

My furnace gas won't come on.
It is a Whirlpool FSB74-125B
The pilot is lit.
Blower will run
The transformer has 120 Volts at each terminal.
 
  #2  
Old 10-02-11, 09:59 AM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
check your 24V transformer.
 
  #3  
Old 10-02-11, 10:11 AM
P
Member
Thread Starter
Join Date: Oct 2011
Location: us
Posts: 3
Received 0 Votes on 0 Posts
The wires at the thermostat also have 120 V. Is this a good indication that the transformer is bad?

If so are these model specific, or is there a generic one I can get?
 
  #4  
Old 10-02-11, 10:55 AM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
Is it for sure a 120 to 24V transformer? if so, I would say yes bad transformer, but I would also say be ready to replace more components....If they were delivered 120V instead of 24V then they might be fried as well.
 
  #5  
Old 10-02-11, 11:01 AM
P
Member
Thread Starter
Join Date: Oct 2011
Location: us
Posts: 3
Received 0 Votes on 0 Posts
yes its a 125 to 24.

The gas valve had 120 volts at the terminals. do you know if thats correct?
 
  #6  
Old 10-02-11, 11:08 AM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,244
Received 2 Votes on 2 Posts
no, typically not correct.... you probably need a new transformer, stat, gas valve, and possibly a relay.... but hard to say until you replace the transformer.
 
 