water dripping from duct


  #1  
Old 01-08-01, 10:33 AM
Guest
Visiting Guest
Posts: n/a
added on central ac 3yrs ago. since first installed
alot of water (condensation) dripping from duct work
which is within a few feet of furnace-a/c unit. any solutions? thanks
 
  #2  
Old 01-08-01, 02:16 PM
PDF
Visiting Guest
Posts: n/a
2 things

Make sure your condensate line is not plugged.If this is the case your blower could be moving condensate down the duct,thus getting to a seam in the duct and leaking.#2 is the duct insulated REAL good?PDF
 
  #3  
Old 01-08-01, 06:03 PM
fjrachel
Visiting Guest
Posts: n/a
Horizontal furnace? Upflow? Package? In the basement? Has happened since day one. Something wrong from the install. Duct work sized correctly? Is it a matched coil? A/C sized correctly?
 
 