furnace wont stay running properly lennox g23, this is going to be a challenge,

hi and hello, i have just bought a home and i think furnace worked fine, but now problem is it will always ignite and run and then shut off, blower keeps going and it will ignite and repeat cycle, it will eventually get to temp after hours of doing this, it should run till it hits desired thermostat temp but it is not, it is like a safety switch is shutting it down, i had to put a new bcc-3 board in yesterday, one of the relays was burnt on it litterally,, took filter out, opened all registers, cleaned everything, i need help, ideas of what to check, i had a half ass repair man out ,he did know good but took my money, i ordered the bcc board and chose that as my first choice and it did the trick from what i had , inducter motor runs, main blower runs, it ignites always just wont run consistent to desired set temp , need some help here, when temp is reached as in now it does shut down completely , any tips would be helpful thanks , also when it does fire and run it only goes full bore for a few minutes, does a cool down i guess as blowers still run , then fires and burns again, it is prob a 1997 yr model it doesnt have code lights to read , it is all mechanical besides for bcc-3 board
 
Sponsored Links
  #2  
Old 01-15-12, 02:50 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,245
Received 2 Votes on 2 Posts
It sounds like you are shutting down on high temp limit. You have already replaced the filter and verified ALL registers are open then you need to verify the evap coil of the air conditioning is clean. This is typically located right above the furnace.
 
  #3  
Old 01-16-12, 01:41 PM
Member
Thread Starter
Join Date: Jan 2012
Location: usa
Posts: 2
Received 0 Votes on 0 Posts
hi

i jumped out thermostat same condition, i went on roof cap and all looks good and clear, i raised a-coil up about 1.5 inches above furnace, air could blast out of there no problem ,all registers are open and took filter out ,, same problem
 
  #4  
Old 01-18-12, 08:23 AM
Member
Join Date: Apr 2011
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
I had the same problem and it ended up where I bought a new thermostat (just a regular, non fancy, honeywell). It cleared up the problem.
 
  #5  
Old 01-18-12, 03:22 PM
Member
Join Date: Jul 2006
Location: Near Philly
Posts: 559
Received 0 Votes on 0 Posts
Does it have a pressure switch and related tubing? Might have intermittent clog in these?
 
  #6  
Old 01-18-12, 03:52 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
Very likely the limit switch is opening because the furnace is overheating.

I'd start by measuring the voltage at the limit switch to verify that the limit switch is open and is shutting off the burners. The best way to do that is to use a multimeter to verify that the 24 VAC shuts off at the limit switch when the burners shut off.


And exposing the AC coil from the bottom and observing airflow coming out of it does no good. The problem is that the AC coil may be plugged with debris and preventing air from freely passing through the coil. If it's plugged you are naturally going to get a strong air flow coming out the gap you created.

You need to lift up the AC coil and inspect it for debris that may be plugging it.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: