Old 01-25-12, 03:55 PM
I have lost heat 3 times this winter. The first time I had the board replaced and the Hot surface ignitor replaced and got heat for about 3 weeks.
The second time I had been hearing this squeeking noise coming from the inducer motor and replaced that. I got heat for another couple of weeks.
Now when I turn on the heat the inducer motor comes on and instead of hearing a click and the hot surface ignitor comming on I get 3 flashes from the green LED indicating a internal error.
I was hoping some one might be able to help me as I am not sure what is causing the internal error and have basically replaced everythign in the furnace now.
Old 01-25-12, 04:19 PM
Grady's Avatar
Received 41 Upvotes on 39 Posts
Usually, but not always, an "internal error" indicates a problem with the furnace control board.
The fact the inducer comes on but the ignition sequence will go no further might point to a pressure switch not closing.
Old 01-26-12, 08:14 AM
V
please post the model and we can look for the info for you.
Old 01-30-12, 12:58 AM
Sure thing. The Number is RGLE-10EQAGS it is a 100,000 BTU Heater.
Also if it is a pressure switch do you know how i can test it???