Bryant 80 plus t inducer motor issues, i think...
Old 01-28-12, 06:00 PM
HI all! I have a bryant plus 80t that's about 13yrs old. A week ago in the middle of the day my Draft Inducer stopped running and in turn the furnace stopped firing up and gives a #31 error for one sequence and then changes to a #32 error. Thinking I'm smart, I ordered a new Draft inducer motor, installed it, and still #31 then #32. I ordered and installed a new dual hi/lo pressure switch assembly, still #31 then #32. I've jumped the limit switch to try get the inducer going, no go. I ran through the sequence test by jumping Test/com24v and get nothing till the Hot Surface Igniter fires up then the blower comes on, but no Draft inducer. Not sure what my next step should be... Suggestions? Thank you!
Old 01-28-12, 06:29 PM
hvactechfw's Avatar
Received 4 Upvotes on 4 Posts
verify voltage to the motor. no voltage = bad control board or connections.
Old 01-28-12, 08:44 PM
SeattlePioneer's Avatar
Received 1 Upvote on 1 Post
This is a good example of why guessing and supposing is not a substitute for a competent diagnostic method.
Hvac tech is pointing the way correctly.
Old 01-29-12, 11:49 AM
Ok, I'm gonna hook up the voltmeter and see what I got...
Old 01-29-12, 04:58 PM
K
While you're there pull out the limit and feel inside to see if your heat exchanger's cracked. My company's replaced about 10 of them on the 80%'s in the past year.
Old 01-29-12, 05:38 PM
hvactechfw's Avatar
not on an 80 + T you have not. on an older 80 yes they were known ofr cracks, but not an 80 + T model
Old 01-31-12, 05:59 PM
K
Oh touche hvactech! You're absolutely right.