Variable speed furnace question
Old 02-13-12, 01:28 PM
C
I recently had a new Tempstar variable speed furnace/ac installed.
Installers did a nice job, however it is not running as it should.
Stat calls for heat, furnace comes on ( at only one speed ), warms house up to desired setting ( new thermostat installed by the same guys ), then shuts off.
Well, I paid for the top of the line unit... being variable speed two stage... but the blower speed does not gear down at any time.
I went to a home show yesterday & talked to 6 or 7 different guys about how a variable speed furnace works and they all said the same thing-- it should operate more often at a lower VARIABLE speed.
I'm thinking that some of the setup (dipswitches ) are not in the proper positions.
Specs... Tempstar # f9mvt0801716a
96% 80,000 btu
White Rodgers/Emerson Thermostat # 1f83-0422
The company that installed this has been in the HVAC business since 1949, so they know their stuff. I'm just afraid that this unit is so new that they may not be completely familiar with how to set this up to operate as it should.
They installed a chimney liner, coil, condensate pump, humidifier, Air Guard air cleaner, the works !
They came back today after talking to somebody at the manufacturer, said they changed some settings. But the unit is still not operating at a lower speed.
Any input would be greatly appreciated...!!
Old 02-13-12, 02:47 PM
hvactechfw's Avatar
Received 4 Upvotes on 4 Posts
are you sure that it is not operating on 1 stage (low) and never needing to go to 2nd stage (high)? This would indicate an oversized furnace, or really low demand due to warmer than normal outdoor temps. Check to see that W2 is wired to the thermostat and furnace.
Here is your install manual. http://www.managemylife.com/mmh/lis_...L/1109764L.pdf
Old 02-14-12, 01:14 PM
C
I checked W2 & it is connected, blue wire on thermostat and on furnace board. When it runs, it is only at one speed (not sure if it is high or low ).
If I increase thermostat 1 or 2 degrees, it indicates "system on".
If I increase it 4,5,6 degrees it indicates "system on +2".
Both cases, blower is at the same speed.
I just think this is a newer unit that the installers may not be as familiar with.
Did I really throw $1000.00 plus away for a "variable speed ECM circulation blower motor" and "two stage self adjusting operation"?
As I understood during initial sales meeting, It will run at a very low (or variable speed ) most of the time to keep the house consistently warm" and ramp up to higher speeds if the temperature drops.
Anything else I can check before calling my guys back ?
Old 02-14-12, 04:09 PM
hvactechfw's Avatar
A volt meter would be necessary to check it thoroughly. DO you have one and know how to use it? Or if not then you would need a set of jumpers.
Old 02-14-12, 05:08 PM
C
Yes, I have both meters and jumpers.
Old 02-14-12, 05:13 PM
hvactechfw's Avatar
ok. Blower door off and door switch taped. Turn thermostat up to call for heat (only 1 degree above room temp). Measure AC voltage between W1 and C and W2 and C. You are looking for 24VAC nominal. At only 1 degree you should only see voltage on W1. IF you turn the stat up more you should see voltage on both W1 and W2. Post your results.
Old 02-14-12, 09:08 PM
user 10's Avatar
Received 57 Upvotes on 50 Posts
The airflow should increase when it upstages.
80k @ 96% afue is a lot of heat - hope your house is large or poorly insulated, otherwise it's oversized.
Old 02-14-12, 09:11 PM
user 10's Avatar
A jumper or dip switch setting may need to be changed to allow the t-stat to control staging.
Old 02-16-12, 01:29 PM
C
25.5v at W1-C
0 at W2-C
Turned thermostat up 4+ deg. & got 26v at W2-C with no change in blower speed.
Old 02-16-12, 01:45 PM
hvactechfw's Avatar
Did the firing rate and inducer speed change?
Old 02-16-12, 01:49 PM
C
I'm not sure what that means. I just went upstairs to turn up stat until "system on" turned to "system on +2", then went back down to check voltage at W2-C.
Old 02-16-12, 02:00 PM
hvactechfw's Avatar
You need a helper to do this properly. Or you need to control at the furnace with jumpers. By being at the furnace you cant tell exactly what is changing it was not changing.