Frame furnace not lighting
Old 03-20-12, 03:20 PM
My furnace igniter seems to heat up but I am not hearing any gas sound. I cleaned the flame sensor and replaced it, because it was acting like a sensor issue. (starts then shuts off). Now it isn't even lighting.
Any help would be awesome
Old 03-20-12, 04:30 PM
It is a TRANE furnace, stupid auto spell
Old 03-20-12, 05:21 PM
hvactechfw's Avatar
Received 4 Upvotes on 4 Posts
is the gas valve switch set to on? What error flash code are you getting from the control board? Do you have a volt meter and know how to use it?
Old 03-21-12, 06:59 AM
2 flashes (lockout from too many attempts)
I checked the gas switch
I have a multi meter.
I am suspecting the gas solenoid. Would a weak igniter possibly cause this also?
Old 03-21-12, 02:45 PM
hvactechfw's Avatar
after the ignitor warms up you should see 24VAC at the gas valve. Typcially there is no such thing as a weak HSI. Depending on the exact model of your furnace you should see 120V applied to the HSI during warm up.
Old 03-22-12, 10:46 AM
SeattlePioneer's Avatar
Received 1 Upvote on 1 Post
After the ignitor heats up for 20-30 seconds or so, the circuit board should switch on 24 VAC to turn on the gas valve for a period of a tleast three seconds. Use your multimeter to measure the voltage across the gas valve to see if that voltage is being turned on.
Just as HVAC Tech suggests....