How do I set pump pressure on Suntec A2VA-3006?
#1
How do I set pump pressure on Suntec A2VA-3006?
I need to set the pressure on a new Suntec Pump A2VA-3006 with the valve on top. Can I hook the gage to the output port by itself, or do I need to add some kind of tee into the line?
I know on the other types of pumps there is a gage port on top, which I have used before.
Thanks in advance.
wingman
I know on the other types of pumps there is a gage port on top, which I have used before.
Thanks in advance.
wingman
#2
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes
on
39 Posts
You can disonnect the nozzle line from the drawer assembly & screw a gauge with a 3/16" flare adaptor into the line. At the firing rate you are using, the difference in flowing pressure & static pressure in minimal (maybe a pound or two) & your gauge won't be that accurate anyway.
Glad you decided to use the 3006 pump instead of the Clean cut.
Glad you decided to use the 3006 pump instead of the Clean cut.
#3
Suntec pump pressure
Thanks again Grady, I appreciate it, and thanks again for the pump recommendation. Sounds like a good idea to have the mechanical backup for the solenoid, just in case.