Furnance wont stay lit

I have a RPJ heat exchanger model GVA100A016DIN. It will ignite ( half of the ignitors) but shut right off.
 
  #2  
Old 09-15-12, 04:48 AM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 5,491
Upvotes: 0
Received 4 Upvotes on 4 Posts
IF only half the burners are lighting then that is why it wont stay lit. There is likely a flame sensor on the last burner that has to be lit to prove successful ignition. It sounds like the burners and crossovers need cleaned. You may want to consider having a professional do this as you are dealing with gas......
 
 