Retrofiting an old Beckett burner with a Cleancut selenoid valve


  #1  
Old 10-09-12, 10:50 PM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Retrofiting an old Beckett burner with a Cleancut selenoid valve

Hi there.

Does anybody know how difficult it is to retrofit an old Beckett burner with a Cleancut selenoid valve?

I have an old Burnham oil burner w/ an old Becket burner. When the burner shuts off, fuel pees into the combustion chamber producing a dull yellow flame that lasts about a minute until the fuel runs out and extinguishes itself. This of course causes sooting throughout the boiler.

I wonder what would it take to install a Cleancut selenoid valve to prevent this from happening.

Moses
 
  #2  
Old 10-10-12, 11:58 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Utterly impossible because there is no such thing as a selenoid valve. The word is solenoid.

If your pump does not cut off cleanly then you have a problem with the pressure regulating valve in the pump.
 
  #3  
Old 10-10-12, 02:28 PM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you Furd (especially for correcting my spelling ).

The pump was replaced in Jan 2012. How can it go bad so quickly?
I will test the pump and replace it if bad. How difficult is to clean it ? is it worthy?

Even after replacing the pump, does it make sense to install a Solenoid valve between the pump and the nozzle assembly to improve clean firing?

Moses
 
  #4  
Old 10-10-12, 05:55 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Don't feel bad about misspelling solenoid, if I had a nickel for every time I have seen that misspelling I could retire. Wait, I AM retired so forget that.

I haven't "monkeyed with" domestic sized oil burners for over thirty years but I personally would not have one that didn't have an oil solenoid valve. Whether or not you can retrofit the Clean Cut valve I don't know. Hopefully Grady will respond as he works with this stuff every day.
 
  #5  
Old 10-10-12, 07:30 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Yep, Grady's here.
I wouldn't give you ten cents for a truckload of Beckett's clean cut pumps unless I could find a sucker to buy 'em. If you want a pump with a solenoid, get a Suntec A2VA-3006. As far as wiring the valve, connect the white to the white of the primary & the colored (purple?) wire to the primary's orange.
 
  #6  
Old 10-15-12, 01:48 PM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
solenoid valve

Thanks much Grady for the suggestions and honest advice !

I ended up installing a stand-alone Carlin valve between the pump and the nozzle assembly (the armature that fits inside the burner). I wired it the way you explained. The burner has been working fine and fuel is not flowing into the combustion chamber anymore

I'm still puzzled why there was a problem in the first place. The pump was replaced this year.

Could it be that the reason is the above ground storage tank?? The fuel level is higher than the pump. Could oil be draining from the tank through the RETURN line through the pump and into the nozzle assembly?

Moses
 
  #7  
Old 10-15-12, 06:36 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
I really can't explain why your pump was allowing oil to trickle thru the nozzle other than the spring valve inside must be shot or crapped up. In any case, the solenoid operated valve is a good idea.

Glad you mentioned you have a return line. Now do yourself & your burner a favor by getting rid of it & installing a Tiger Loop in the line between the filter & the burner. Having a 2 pipe system means you are blowing oil thru that filter at aprox. 34 times as fast as you are burning the oil. Slow down that flow & the filter will do a much better job.
 
  #8  
Old 10-16-12, 09:09 AM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
Getting rid of return line w/ Tigerloop

Roger that Grady,

I ordered a Tigerloop kit online and will install it when it arrives. The local store had one but wanted $240 for it (bio model). I got the basic model online for about $90 and free S&H. I burn Diesel No 1.

34x as fast?? no wonder last year the lines and filter and pump and even some part into the nozzle assembly were covered with about 1 inch of ice !!! The pump was pulling -20F oil so fast.

THanks for the advice. I'll report as soon as I get and install the tigerloop.

Moses
 
  #9  
Old 10-16-12, 02:42 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
In your case 34x is about right. When using a 2 pipe, you pump oil at the full capacity of the pump's gear set, which in the case of a Suntec A2VA-7116 is about 17 gallons/hour.
 
  #10  
Old 11-04-14, 03:22 PM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tigerloop metric ports

Hello,

Does anybody know what size thread are the Tigerloop ports. They look like 3/8 standard thread but they aren't. They look metric.

Moses
 
  #11  
Old 11-04-14, 04:35 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Tigerloop threads are 1/4" female pipe thread. Do not use teflon tape or a pipe joint compound containg teflon. I prefer #2 Permatex.
 
  #12  
Old 11-05-14, 02:45 PM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tigerloop threads

Grady,

I know that Tigerloop specifies 1/4" pipe thread but using a normal 1/4" male fitting I can only turn a couple of turns by hand. However, the fitting that comes w/ the the Tigerloop hoses goes in about 5 turns freely.

So I compared the threads of the Tigerloop hose fitting w/ a normal 1/4" male pipe fitting and noticed that the threads begin to offset slightly after 4'th thread or so, which makes me think that it's really metric even if advertised as 1/4" female pipe thread.

Is it alright to just a 1/4" male pipe fitting and tighten the connection as much as possible (maybe 3 or 4 turns)? It just doesn't seem right to do this.
 
  #13  
Old 11-05-14, 02:58 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
The threads could be BPT (British Parallel Thread). When I've hard piped or used copper on a Tigerloop, I've never had any problems with leaks using ordinary NPT fittings.
 
  #14  
Old 11-05-14, 03:47 PM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tigerloop port fittings

Thanks Grady,

Do you think it'll be OK to use brass (instead of copper) fittings a sealant compound to connect fittings to the tigerloop and tighten the connections as much as possible (3 turns or so)?
 
  #15  
Old 11-05-14, 04:21 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
If you are using copper tubing, the fittings will be brass. Just remember to use a back up wrench on the Tigerloop. Also remember you are going into aluminum.
 
  #16  
Old 11-05-14, 05:17 PM
M
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 13
Upvotes: 0
Received 0 Upvotes on 0 Posts
Tigerloop fittings

Ok THanks for your help Grady !
 
 