Oil burner starts & runs when not required

I have an oil burner for hot water baseboard heat + supplies hot water to faucets.

It occasionally starts and moves hot water through heating pipes when the temperature settings on each of the 3 zone thermostats are set lower than the current temperature.

While I'm unlikely to attempt D-I-Y repair, I would like to know the possible causes.

Thanks in Advance!
 
  #2  
Old 10-26-12, 11:44 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,499
Received 4,059 Upvotes on 3,642 Posts
If it just starts by itself it could be a thermostat. You'll need to determine which zone is calling for heat so you know where to start looking.
 
  #3  
Old 10-26-12, 12:45 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 39 Upvotes on 31 Posts
Because your boiler has a tankless coil to supply domestic hot water it needs to maintain a certain minimum temperature inside the boiler at all times. If it is also running the circulator pump then you have a control problem. It is most likely the setting of the minimum temperature circulator control although if it only happens on an intermittent basis it could be a sign of imminent control failure.

Posting several pictures of the controls on your boiler might help us to pinpoint the exact cause.
 
  #4  
Old 10-26-12, 01:01 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,993
Received 85 Upvotes on 77 Posts
Just a note it could be one of the flow controls also. ( Only if you have circs and not zone valves.)
 
 