Gibson furnace only one jet fires

I have a Gibson model #KG7A045C-23A

after igniter fires the jet next to it lights up for a couple seconds, the other two do not, igniter goes out flame dies
Cleaned out all three jets
increased pressure on gas valve one 1/4 turn
Same thing

could this be the gas valve or the igniter?
 

Last edited by Buz51; 10-31-12 at 05:39 PM.
  #2  
Old 10-31-12, 07:13 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 5,491
Upvotes: 0
Received 4 Upvotes on 4 Posts
no, likely the burner and crossovers need cleaned or repositioned. You should NEVER adjust a gas valve without a manometer and it should be done by a pro. A 1/4 tun is a lot more than you think!
 
  #3  
Old 11-01-12, 04:00 PM
B
Member
Thread Starter
Join Date: Oct 2012
Location: usa
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
I cleaned the burner and crossover.
That did the trick
Thanks for your help
 
 