Heil GH-100AE-7R gas furnace with issues Please Help!

Hello, I have a old Heil with the following symptoms.
When the thermostat sends a signal to kick on the furnace:
1. The burners come on and heat for approx 4 minutes.
2. At this point the blower is off.
3. The blower then comes on.
4. When the blower comes on the burners go off.
5. After 60 seconds with the blower running the burners come on and light with a "whoosh" that sends the flame outside of the furnace.
6. It runs fine until the tempurature is met.

I had a service guy come by today to tell me this was "normal" and charge me $220.00

Is this normal?

Here is the sequence of events in real time hh:mm:ss

10:02:50 Burner comes on, blower is off
10:05:43 Burner turns off, blower turns on
10:06:45 Burner comes on, blower remains on

Ignition and "whoosh" flames shoot out of the furnace.


Any HVAC gurus that can comment?
 

Last edited by HyattHyatt; 12-03-12 at 07:21 PM.
Sponsored Links
  #2  
Old 12-04-12, 03:13 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
Do you have a multimeter and understand how to measure 24 VAC and 120 VAC with it?
 
  #3  
Old 12-04-12, 04:44 AM
Member
Thread Starter
Join Date: Dec 2012
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Yes, I have a Mulitmeter. What do I need to test?
Could the "rollout" be due to to much gas pressure to the burners?
If so, is this adjustable? And how?
Thanks for the reply.
 
  #4  
Old 12-04-12, 08:55 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Received 0 Votes on 0 Posts
Using the furnace sheet metal as a ground, connect one test lead to ground and set you meter to read 24 volts AC or more.

Use the other test lead to see if the 24 volts from the pressure switch is shutting off when the burners turn off.

What is the model number of the furnace from the rating plate in the burner compartment?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: