4 flashing lights on Winchester by Hamilton

I have a Winchester (hamilton) G8t08012uha11a model.

the Unit will start up the fan motor kicks in but no heat will come out of the vents. The indicator lights flash 4 times fast. the panel say it is a high aux or spill switch open.
 
Sponsored Links
  #2  
Old 12-09-12, 01:07 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Check your switches to see if they are open.. If they are open then something has caused this to do this..

High Aux- Heat exchanger got hot from poor air flow from either dirty filter, or vents blocked/closed.

Spill switch- Blocked flue pipe or heat exchanger.. Burner issues.
 
  #3  
Old 12-10-12, 01:20 PM
Member
Thread Starter
Join Date: Dec 2012
Location: usa
Posts: 2
k check flue it is open as far as i can see
the motor is firing n igniting n the intake motor is turning but we are getting low air flow from the vents

cleaned all the vents around the motor to ensure correct air intake
 
  #4  
Old 12-10-12, 04:46 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
"Getting low air flow from vents"

You mean you are getting weak air blowing out of your vents in the home? What happens if you switch the fan switch on the t-stat to "ON"?
 