Trane XL90 Problems...No Ignition

I was able to solve my Trane XL90 ventilation pressure sensing problems last year, now my upstairs unit is acting up. ( http://www.doityourself.com/forum/ga...problem.html#b )

This time I don't think it is going to be so easy. The pressure switch is working ok and I get clicking but no ignition. I'm not home now but this evening I'll be checking the ignitor. From what I read it is 24V.

I found some related threads with things to try: ( http://www.doityourself.com/forum/ga...problem.html#b )
Thread with pictures of limit switch on same model ( On a Trane XL90 furnace, igniter comes on and stays on for - JustAnswer )
 
Sponsored Links
  #2  
Old 12-13-12, 12:35 PM
Forum Topic Moderator
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 4,296
Upvotes Received: 1
I'm pretty sure that your hot surface ignitor is 120 VAC, not 24 Volt. I had one last six years, another run less than a year, and my current one is going on ten years.
 
  #3  
Old 12-13-12, 03:56 PM
Member
Thread Starter
Join Date: Mar 2011
Location: usa
Posts: 12
Yes, thanks 120v and this is showing correctly. So, I removed the ignitor and it is fractured. I have a new one and a spare for the other furnace to pick up tomorrow at a local Grainger warehouse.
 