Boiler circulator stays on even when thermostat set below 50.


  #1  
Old 12-15-12, 03:18 PM
F
Member
Thread Starter
Join Date: Dec 2012
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Boiler circulator stays on even when thermostat set below 50.

Burnham propane furnace, forced hot water, 3 zones. One zone circulator pump stays on regardless of setting. Only way to shut down is emergency switch. Other zones "click" on & off with thermostat change. Honeywell RA832 relays on each zone. One stays "on" when power applied. Other 2 work fine with thermostats. Do I need a new relay or could there be other problems that can be checked & fixed on site? Installed 18 years, only two circulators replaced & exhaust flue vent malfunction once in that time.
 

Last edited by Fortboy; 12-15-12 at 03:37 PM.
  #2  
Old 12-18-12, 03:44 PM
F
Member
Thread Starter
Join Date: Dec 2012
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Problem fixed by service man. Two wires touching behind thermostat closed the circuit and kept "calling" for heat.
 
 