Trane (American Standard) Gas Furnace Not Working After Power Failure


  #1  
Old 12-17-12, 07:07 PM
T
Member
Thread Starter
Join Date: Dec 2012
Location: United States
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Trane (American Standard) Gas Furnace Not Working After Power Failure

Had an instantaneous power failure a few days ago, and the heat stopped working. The troubleshooting light flashes 9 times indicating hot surface igniter or ground issue. I examined the HSI and saw that both wires from the connector to the HSI were literally "fried". The insulation was burned almost completely off of the wires.

So, I replaced it with an OEM Trane IGN00145 HSI. It briefly glows (just for a second or two) and then shuts off. The draft inducer fan also turns on but only for a few seconds. I do not smell gas and the burners do not light. The furnace is an American Standard UD100C945J.

My natural gas supply is ok. My gas water heater is nearby and is working fine.

Any suggestions are most welcome and appreciated.

 
  #2  
Old 12-17-12, 07:20 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,897
Received 3,752 Upvotes on 3,364 Posts
After replacing the HSI do you still get the 9 flashes ?
 
  #3  
Old 12-17-12, 07:32 PM
T
Member
Thread Starter
Join Date: Dec 2012
Location: United States
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes. I neglected to say that.
 
  #4  
Old 12-17-12, 08:42 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
Replace the circuit board/ignition control.

You have a fired board.
 
  #5  
Old 12-17-12, 10:08 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 5,491
Upvotes: 0
Received 4 Upvotes on 4 Posts
I have to agree, but beware you may have more damage than that. An electrical surge can cause things like this and can affect multiple components in the furnace.
 
  #6  
Old 12-18-12, 07:42 AM
T
Member
Thread Starter
Join Date: Dec 2012
Location: United States
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the replies. I ordered a new circuit board and will post results hopefully later this week.
 
  #7  
Old 12-18-12, 04:30 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
All too true, HVAC tech!
 
  #8  
Old 12-22-12, 03:16 PM
T
Member
Thread Starter
Join Date: Dec 2012
Location: United States
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Unhappy Replaced the cirucit board, but other problems

Okay, I replaced the circuit board and fired it up. The system fired up, and I thought it was fixed.

Not so, it melted the insulation on my new HSI, and now I'm getting the 9 flashing lights again.

Any suggestions what is frying the wires? I don't know if the new circuit board is ruined.

These things will break your heart!
 
  #9  
Old 12-22-12, 03:33 PM
T
Member
Thread Starter
Join Date: Dec 2012
Location: United States
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Unhappy Tried again after HSI wires fried

I got the nerve up to try the furnace again after noticing the HSI wiring insulation was burned after replacing the circuit board.

To my surprise the furnace fired up for the second time. I still don't know what to think about the burned insulation and how long the furnace will continue to operate under the circumstances.

Is it possible the heat from the furnace flames are burning the insualtion, or is it an electrical problem?

I assume the new circuit board is okay so far since the system is working (for the moment).
 
  #10  
Old 12-22-12, 06:40 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 5,491
Upvotes: 0
Received 4 Upvotes on 4 Posts
you need to watch the flames to make sure they are not burning up the insulation, but I doubt it is that unless you bought an aftermarket HSI with improper wire insulation.
 
  #11  
Old 12-22-12, 08:39 PM
T
Member
Thread Starter
Join Date: Dec 2012
Location: United States
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Correction - HSI is IGN00145

It's not an aftermarket HSI. It's a Trane IGN00145. Since the insulation is burned off, I doubt I will be able to tell if furnace heat is melting it.
 

Last edited by tchad09; 12-22-12 at 08:43 PM. Reason: Typo error
  #12  
Old 12-22-12, 09:28 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 5,491
Upvotes: 0
Received 4 Upvotes on 4 Posts
I would check voltage to the HSI and the amp draw with a clamp on meter.
 
  #13  
Old 12-23-12, 08:54 PM
T
Member
Thread Starter
Join Date: Dec 2012
Location: United States
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'm not sure how I would check the proper voltage on the HSI? It's an 80v silicon nitride HSI, so what voltage should the cirucit board provide to it?

I took the HSI out today to further inspect the burned wiring insulation. The insulation on both wires is only burned off about 1/3 of the way down from the ceramic portion of the HSI. The other 2/3 of the insulation (on both wires) down to the plastic connector looks ok.
 
 