While visiting my Mom for the holidays, we've been having trouble with her furnace and I haven't come across any good information about this problem or how to fix it.
When the thermostat calls for heat, the inducer/combustion motor cycles off and on several times before the ignitor kicks in. Once I have a flame, there are no other problems. It's pretty annoying hearing the relays clicking so much, but that seems to be the only problem.
Before this, I have already cleaned the flame sensor which was looking a little grimy. I've also checked for any error codes and came up empty. The LEDs show that everything is operating normally.
Any ideas?
Old 12-29-12, 09:15 PM
Houston204's Avatar
Received 89 Upvotes on 82 Posts
I'd check the stat.
Does the furnace start normally if you remove the stat and jump R (24VAC) to W (heat terminal)?
Old 12-30-12, 01:43 PM
SeattlePioneer's Avatar
Received 1 Upvote on 1 Post
When the thermostat calls for heat, it does so by taking voltage from the R terminal on the furnace and applying that voltage to the W terminal on the furnace.
Any time you have 24 VAC being applied to the W terminal the inducer motor should turn on and stay on.
So the proper way to check what is happening is to use a multimeter to see if the inducer motor is staying on when there is 24 VAC to the W terminal.
If you do, that suggests that the thermostat isn't switch on voltage to the W terminal reliably, or perhaps the voltage to the R terminal is being interrupted.
If the voltage to the W terminal is on and the inducer motor isn't starting and staying on reliably, you have a bad circuit board that needs to be replaced.