Rheem Gas furnace Model # RCBA 3765GG17 GAS IS NOT COMING ON

The thermostat is working, the ignitor thing is glowing, no gas is coming into the furnace, please help with any advice.
Thank you so much in advance for any help.
 
  #2  
Old 12-31-12, 01:52 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
After the ignitor heats up for 30 seconds or so, the ignition control module should turn on the 24 VAC to the electric gas valve which will cause gas to flow to the burners where it will be lit by the HSI.

If that's not happening, first check to be sure you have gas to the gas valve. All the gas valves should be open and the dial on the electric gas valve turned to on. Do you have other gas appliances and are they operating normally?

Once you are sure you have gas, use a multimeter to check to see if you have 24 VAC being switched on to operate the electric gas valve after the HSI heats up. If you do, you may have a bad gas valve.

If you don't, you may have a bad ignition control module.
 
 