Gas fired boiler will not fire up. Pilot is lit.


  #1  
Old 01-04-13, 05:39 AM
G
Member
Thread Starter
Join Date: Jan 2013
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Gas fired boiler will not fire up. Pilot is lit.

Crown Aruba Series Model ABF-SPD Continuous Pilot.

“Pilot is lit”

When emergency switch is turned on and off the following accrues.

Damper opens.

Circulator pumps is on.

Thermostat is calling for heat.

(no igniting of flame)

However when I run a jump wire from aquastat ( T ) 24v
to the Gas value - fires up.

What is the cause of this?

Thank you.
 

Last edited by lawrosa; 01-04-13 at 07:47 AM. Reason: fixed quote brackets
  #2  
Old 01-04-13, 06:13 AM
N
Member
Join Date: Jan 2012
Location: Canada
Posts: 2,511
Received 21 Upvotes on 18 Posts
Sounds like a relay in your aquastat is going or gone bad.

I am a bit concerned about the bit about the emergency switch being turned on and off. If I'm reading your post correctly, the circulation pump(s) and dampener still operate when this switch is on or off?
 
  #3  
Old 01-04-13, 06:40 AM
G
Member
Thread Starter
Join Date: Jan 2013
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Mike - Thank you.

The emergency switch was manually being turned on and off by me.

I wanted to explain clearly how it was operating.

Thank you again.

Q) So I would have to replace the complete Aquastat?

All the best Gary
 
  #4  
Old 01-04-13, 07:32 AM
N
Member
Join Date: Jan 2012
Location: Canada
Posts: 2,511
Received 21 Upvotes on 18 Posts
I suspect replacing the whole aquastat.
What is the make/model of the actual aquastat?
 
  #5  
Old 01-04-13, 07:51 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,993
Received 84 Upvotes on 76 Posts
The damper may not be opening all the way or end switch failure. Not sure which one you have but there should be a switch to manually open it. Put it on manual and try to fire the boiler.

Do you have a multimeter and know how to use it?

I will post back with the manual and trouble shooting tips.

I dont think its the relay if the circ is running......
 
  #6  
Old 01-04-13, 08:01 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,993
Received 84 Upvotes on 76 Posts
Here is the manual. I will locate the Effikal manual since thats the damper you have I believe.



http://www.crownboiler.com/manuals/c...l_Models/Aruba (ABF-SPD, ABF-EID).pdf


Here is a recall on effikal but I dont think your boiler is there.


Recall Program


Website with schematic.


Gas Vent Damper - Efficiency - Specifications

PDF

http://fieldcontrols.com/pdfs/46352700.pdf
 

Last edited by lawrosa; 01-04-13 at 08:42 AM.
 