Burner but no fan

I have a carrier model 48SD and when I turn it on the burner starts fine but then the fan does not start. I have waited several minutes and it still does not run. If I turn it off and start all over again it will run just fine. It also will work fine for a long time and then for no reason it will call for heat and the fan will not start again. I am not sure what is wrong and hope someone can tell me what to repair, thanks.
 
  #2  
Old 01-14-13, 07:49 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,935
Received 3,950 Upvotes on 3,543 Posts
You'll need to determine if it's a control board problem or a blower motor problem.

When the fan does not start......try putting the AUTO/FAN ON switch in FAN ON mode and see if fan works then. If it doesn't come on then you have a blower motor issue......possibly a defective starting capacitor.
 
  #3  
Old 01-16-13, 05:30 PM
Y
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
I waited till the problem happened again the fan was not working so I turned the fan on and it started so I guess it is not the fan. Any other thoughts before I get a new board.
 
  #4  
Old 01-16-13, 05:57 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,935
Received 3,950 Upvotes on 3,543 Posts
Most furnaces use a heat thermostat to turn the blower on. Yours does not. It's a timed function controlled by the control board. Based on the service schematic I would say it's a defective control board.


The board.....part # 325878-751 is pretty pricey.

I would wait for a confirmation from one of the HVAC guys.
 
  #5  
Old 01-16-13, 06:29 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
http://www.docs.hvacpartners.com/idc...t/48sd-5si.pdf

I agree, it's a faulty control board.

 
  #6  
Old 01-16-13, 06:39 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,935
Received 3,950 Upvotes on 3,543 Posts
Wow.... cool colored schematic.
 
  #7  
Old 01-16-13, 06:47 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
Thanks.

I'm surprised to see a direct drive multispeed motor in a Carrier gas unit use the same speed for heating and cooling.

I looked up the 48GS that this unit resembles and it is the same.
 
  #8  
Old 01-16-13, 06:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,935
Received 3,950 Upvotes on 3,543 Posts
You are correct....same speed.....which is very unusual.
 
 