Draft? fan pluses several times before furnace fires up

I have a Goodman GMNT Gas furnace. When it is starting up, the fan motor starts and runs for 5-10 seconds, then turns off. After a few seconds, it comes on again. After a few cycles, the furnace finally ignites.

Should I Be concerned? It’s been doing this for some time now. I would appreciate ideas on how to troubleshoot the problem.
Thanks
 
  #2  
Old 01-21-13, 10:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,930
Received 3,758 Upvotes on 3,369 Posts
By fan motor do you mean the draft inducer blower. The little one in the exhaust line ?

What it's doing doesn't sound normal.
 
  #3  
Old 01-22-13, 12:28 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
The inducer motor should turn on and stay on as long as the thermostat is calling for heat, or more specifically whenever there is 24 VAC applied to the W terminal on the furnace.

I'd check to see if the thermostat is staying on by using a multimeter to check on that voltage. If the voltage is present and the inducer motor isn't staying on, yes, your should be concerned.

Either the inducer motor is fail;ing or the circuit board is failing to turn the inducer motor on properly, and this will likely progress to failure of the furnace to light.
 
 