carrier 58 pav 131 upflow won't run
my carrier 58 pav 131 upflow furnace won't start - no power to inducer draft motor- checked inducer motor =runs fine - no power coming from board- shows code 31 - reset dss switch and main blower runs but no inducer and no heat - thanks
#2
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
carrier 58 pav 131 upflow won't run
my carrier 58 pav 131 upflow furnace won't start- code 31- inducer motor won't start- by passed and ran inducer motor- works perfect- no power coming from mother board - shows code 31- reset dss switch and main blower came on and runs but no inducer draft so no heat - thanks
#4
The inducer motor should run when the thermostat is calling for heat.
Since the furnace will run when you independently power the inducer motor, the thermostat should be turning on the furnace OK.
That means you need to replace the ignition control module which is failing to turn on the inducer motor properly.
Since the furnace will run when you independently power the inducer motor, the thermostat should be turning on the furnace OK.
That means you need to replace the ignition control module which is failing to turn on the inducer motor properly.
#5
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
carrier 58 pav131
​[TABLE="width: 500"]
[TR]
[TD][/TD]
[TD][/TD]
[/TR]
[TR]
[TD][/TD]
[TD][/TD]
[/TR]
[TR]
[TD][/TD]
[TD][/TD]
[/TR]
[/TABLE]
​
[TR]
[TD][/TD]
[TD][/TD]
[/TR]
[TR]
[TD][/TD]
[TD][/TD]
[/TR]
[TR]
[TD][/TD]
[TD][/TD]
[/TR]
[/TABLE]
​
- the furnace did not run when I powered up the inducer draft motor- I just un did the wires and connected an extension cord to the motor and it ran fine- when you turn the thermstat on nothing happens- if I reset the dss switch the main blower motor starts- but inducer motor does not start- did the test proceedure and ignitor came on and main blower ran but no inducer motor- jumped a drop light to the motherboard to see if power was coming out of it to inducer motor when thermostat is tripped but does not send power to inducer- thanks
#6
Use a multimeter to check the following, in order:
Check to see if you have 24 VAC between the R and C terminals when the 120 VAC is switched on to the furnace.
This verifies that you have low voltage power.
Check to see if you get 24 VAC between the W and C terminals when the thermostat is turned up.
If you do, this proves that the thermostat is switching on the furnace.
If you have 24 VAC to the W terminal, the inducer motor should turn in and stay on.
Since you have already verified that the inducer motor is OK, that would mean that the ignition control module is failing to turn on the inducer motor, and the ignition control module needs to be replaced.
Check to see if you have 24 VAC between the R and C terminals when the 120 VAC is switched on to the furnace.
This verifies that you have low voltage power.
Check to see if you get 24 VAC between the W and C terminals when the thermostat is turned up.
If you do, this proves that the thermostat is switching on the furnace.
If you have 24 VAC to the W terminal, the inducer motor should turn in and stay on.
Since you have already verified that the inducer motor is OK, that would mean that the ignition control module is failing to turn on the inducer motor, and the ignition control module needs to be replaced.