furnace keeps shutting down mid cycle - electrodes appear sooted
#1
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 94
Upvotes: 0
Received 0 Upvotes
on
0 Posts
furnace keeps shutting down mid cycle - electrodes appear sooted
heres an older pic I took of the electrodes inside. I've since re-adjusted them a bit so they sit higher

I question the condition of them, as well as the curve in their tip, all of the images I've seen online so far have straight bends as up posed to the curve, and they angle towards each other upposed to pointing like these do.
the soot is allways generally hanging between the two tips.


I question the condition of them, as well as the curve in their tip, all of the images I've seen online so far have straight bends as up posed to the curve, and they angle towards each other upposed to pointing like these do.
the soot is allways generally hanging between the two tips.
#3
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,674
Received 40 Upvotes
on
38 Posts
Grady, the old oil burner geezer is here. Electrode tips should be NO more than 1/2" above the nozzle. I prefer to keep them around 7/16". They should also be no more than 1/8" in front of the nozzle face & 1/8" apart.
That is an OLD burner. What make? Electrodes look like a Nu-Way.
If that burner is in a furnace (not boiler) I'd have the heat exchanger checked.
That is an OLD burner. What make? Electrodes look like a Nu-Way.
If that burner is in a furnace (not boiler) I'd have the heat exchanger checked.
#4
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 94
Upvotes: 0
Received 0 Upvotes
on
0 Posts
the burner is a bottom firing. the electrodes are about 3/8 away from the nozle, 1/8 above it , and about 1/8 gap currently.
I have been suspicious of the heat ex changer given the furnace vibrates/rattles in that area when it's first starting up.
Guess after I force it through this year I'll have to retire it.
What is a good price/reliability balanced brand for a lowboy furnace ? I want to adapt it to my current duct work.
the furnace is in the basement, and the house has two Upper stories. The plenium currently has 5 branches out of it.
I have been suspicious of the heat ex changer given the furnace vibrates/rattles in that area when it's first starting up.
Guess after I force it through this year I'll have to retire it.
What is a good price/reliability balanced brand for a lowboy furnace ? I want to adapt it to my current duct work.
the furnace is in the basement, and the house has two Upper stories. The plenium currently has 5 branches out of it.
#5
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,674
Received 40 Upvotes
on
38 Posts
You may be getting the electrodes into the spray pattern of the nozzle. Set the electrodes as follows & try it. 7/16" above the nozzle center, 1/16 to a max of 1/8" ahead of the nozzle face, & a fat 1/8" gap.
There are several decent oil fired lowboys out there. Top of the heap is Thermo-Pride. Boyertown Furnace makes good stuff as well (Rheem is now made by Boyertown). Armstrong or Ducane aren't bad nor is Heil or Tempstar.
There are several decent oil fired lowboys out there. Top of the heap is Thermo-Pride. Boyertown Furnace makes good stuff as well (Rheem is now made by Boyertown). Armstrong or Ducane aren't bad nor is Heil or Tempstar.
#6
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 94
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I should probably note that this furnace fires oil upwards out of the bottom of the chamber as upposed to the burner itself.
I adjusted the electrodes so they are 1/16 (also tried 1/8) above the nozzle height/face 7/16 away from and 1/8 apart.
when the electrodes were 1/8 above the nozzle they sooted very fast and the furnace refused to restart until I cleaned them.
also furnace seemed to run longer when I had the tips gaped at 1/4th apart
The furnace is still shutting off the burner after running approx 5 -10 minutes.
the electrodes still appear sooted but the furnace restarted with the reset 19/20 times.
the airflow (house side blower continues to run till the unit is cool)
The unit appears to be burning when It trips the stack reset.
could the electrodes be setup so their tips are flush height with the nozzle?
I adjusted the electrodes so they are 1/16 (also tried 1/8) above the nozzle height/face 7/16 away from and 1/8 apart.
when the electrodes were 1/8 above the nozzle they sooted very fast and the furnace refused to restart until I cleaned them.
also furnace seemed to run longer when I had the tips gaped at 1/4th apart
The furnace is still shutting off the burner after running approx 5 -10 minutes.
the electrodes still appear sooted but the furnace restarted with the reset 19/20 times.
the airflow (house side blower continues to run till the unit is cool)
The unit appears to be burning when It trips the stack reset.
could the electrodes be setup so their tips are flush height with the nozzle?
Last edited by kiyolaka; 02-12-13 at 12:16 AM.
#7
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,674
Received 40 Upvotes
on
38 Posts
Once the flame ignites, the ignition system (electrodes), should be out of the picture. With most OLD equipment and all new burners the ignition drops out after flame is proven. You have another problem besides the electrodes. Without being able to spend time with it & see first hand what the burner is doing, it's going to be darned tuff to trouble shoot. Do you have a volt meter & know how to use it?
#8
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 94
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes, I do electronics repair as a bit of a hobby/cheap way to fix stuff and get it for my house.
I also happen to own a cheap Endoscope.
before we go too much further could a restricted/failing heat ex changer be the issue?
When I vaccumed the stack duct it was absolutely filthy, had about 3/8 of an inch of slit throughout the entire thing, and the stack control spring was sitting almost directly on the stuff.
so it would not surprise me if the heat ex changer is full of it too.
Other than that my uneducated guess is perhaps the stack control unit is malfunctioning?
I also happen to own a cheap Endoscope.
before we go too much further could a restricted/failing heat ex changer be the issue?
When I vaccumed the stack duct it was absolutely filthy, had about 3/8 of an inch of slit throughout the entire thing, and the stack control spring was sitting almost directly on the stuff.
so it would not surprise me if the heat ex changer is full of it too.
Other than that my uneducated guess is perhaps the stack control unit is malfunctioning?
#9
Just checking. Have you checked you oil supply. If the furnace comes on and rumbles that may be your problem. You need a nice clean oil supply with no air in the line and the pump pressure should be between 90 and 100 psi.
#10
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 94
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Psi is approx 97 when I last checked. I've bled the system quite a bit at the pump as well as at the filter. as well as replaced the tubing between the pump and nozzle (old flare had small crack in it.
pump strainer,nozzle and filter cartrige are all new.
It does still occasionnaly rumble though, especially if I turn down the burner airflow (currently its at approx 80% of its max)
pump strainer,nozzle and filter cartrige are all new.
It does still occasionnaly rumble though, especially if I turn down the burner airflow (currently its at approx 80% of its max)
#12
Sounds like you need the complete vac. and brush,clean and restep stack stack relay if not a new one,adjustments of electrodes and burner. Your better off, it looks like a mess.
#13
Member
Thread Starter
Join Date: Nov 2011
Location: USA
Posts: 94
Upvotes: 0
Received 0 Upvotes
on
0 Posts
stack control was toast, replaced and have not had an issue since.
also appearantly with this particular furnace being a one of a kind bottom vortex burner design, it has a bit of a unique gaping for the electrodes. Closer to 1/2 from nozzle center (it fans out more than 80* due to the vortex airflow) Flush with the nozzle height wise, and slightly more than 1/8 gap.
also appearantly with this particular furnace being a one of a kind bottom vortex burner design, it has a bit of a unique gaping for the electrodes. Closer to 1/2 from nozzle center (it fans out more than 80* due to the vortex airflow) Flush with the nozzle height wise, and slightly more than 1/8 gap.