Nordyne G6RA 80+ Furnace - red light flashes once, no heat, blower continuous

No heat today - red light w/ 1 flash (= Limit Circuit Open or External Load on "W"). Thermo fan is on "Auto", Temp is "off" , but blower still runs.
I cut power at panel for 1 minute, turned breaker back on, and within 5-6 seconds the fan came back on again. Still no heat, still single flash.


And, oh, by the way, it's Sunday, of course
-Dennis
 
Sponsored Links
  #2  
Old 02-10-13, 10:58 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
What type of air filters do you use?
Is the air filter clean now?
Do you have a meter?




Looks like you have a vent safety switch and a roll-out on the limit circuit, they usually have manual reset buttons. We would also need to verify why it tripped.
 
  #3  
Old 02-10-13, 11:24 AM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Huston204: I have a fairly inexpensive fliter - cleaned 10 days ago. I did have an issue once w/ a too-dirty filter (which I cleaned/replaced, and it solved the problem), but this seems to be a different issue. I did try to reset the vent safety switch - to no avail.

We do have a meter - it's a Sears 982361. Never really used it.
 
  #4  
Old 02-10-13, 11:36 AM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
UPDATE: We pushed the Roll-out switch, it reset, I turned power off then on (because the fan was still going), and now it is working again.

What would cause the roll-out switch to trip??
 
  #5  
Old 02-10-13, 11:49 AM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
UPDATE #2: It tripped again, and I now have the blinking red light again. It did bring it up to temp, however, before it shut off. Fan is still blowing (but it's not turned on at the stat).
 
  #6  
Old 02-10-13, 11:57 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
The most likely cause for a roll out switch to trip is a crack, hole or restriction in the heat exchanger.

Sounds like its time to call a pro.

 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: