Propane furnace exhaust blower cycles on/off - thermostat NOT calling for heat

Propane furnace exhaust blower cycles on/off - thermostat NOT calling for heat

Reply

  #1  
Old 02-24-13, 10:12 AM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Votes on 0 Posts
Question Propane furnace exhaust blower cycles on/off - thermostat NOT calling for heat

Hi,

The exhaust blower on our furnace has started cycling on/off continuously when the thermostat is NOT calling for heat. If I turn off thermostat, it stops. If I set thermostat to heat, it seems to function normally - i.e., exhaust blower will immediately start running constantly, gas solenoid will trip, furnace will ignite, and main blower will start. But then when heat has been satisfied and room temperature is below thermostat set-point, exhaust blower will once again start cycling on/off every 3 seconds or so.

Just to clarify, this is the small exhaust blower that vents to the outside, not the main furnace blower.

Any ideas? Thanks!
 
Sponsored Links
  #2  
Old 02-24-13, 10:44 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,930
Received 262 Votes on 247 Posts
That is called a draft inducer blower.

It should only run when the thermostat calls for heat. You said when you turn the thermostat off it doesn't cycle. How do you turn a thermostat off ? The OFF between heat and cool ?


This problem has appeared here recently and I don't think we were able to determine what was causing it.
 
  #3  
Old 02-24-13, 10:54 AM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Votes on 0 Posts
Yes, if I physically switch the thermostat to off (between heat and cool) the draft inducer blower stops cycling. But of course, this leaves us without a furnace that functions independently.

The thermostat is digital, made by Hunter. I replaced the batteries yesterday. It is at least 10 years old. The furnace is ~19 years old.

Thanks!
 
  #4  
Old 02-24-13, 12:49 PM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Votes on 0 Posts
Do you think this could be an issue with the thermostat? I have a multimeter - is there anything I can trouble-shoot?
 
  #5  
Old 02-24-13, 12:55 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 5,503
Upvotes: 0
Received 0 Votes on 0 Posts
Sorry--- your comments are too vague to be of any use in identifying the problem.


Describe in detail and in order the sequence of events that occurs when you turn up the thermostat to call for heat.

Describe in detail what happens when you turn the thermostat doesn so that it isn't calling for heat.
 
  #6  
Old 02-24-13, 01:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,930
Received 262 Votes on 247 Posts
S.P. This problem crops up every once in a while. It almost seems like the thermostat is creating just enough of a load to activate the draft inducer blower but not enough to cause the burners to light. I know...sounds crazy.
I was trying to dig up some of the other threads. In the other thread the OP claimed he replaced the thermostat and yet it still had the problem......and on more than one unit too.
 
  #7  
Old 02-24-13, 01:14 PM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Votes on 0 Posts
Yes, and just to clarify:

When the thermostat is calling for heat, there is no problem whatsoever (as far as I can tell). The furnace, including both blowers, functions normally.

The problem is ONLY when the thermostat is NOT calling for heat. That is when the draft inducing (exhaust) blower cycles on/off every 3 seconds or so. It does this continuously. The only way to quiet it is to turn the thermostat off, and by "off" I mean, slide the heat/cool switch to the middle (off) position.

So, even taking into account the experience of the other poster, do you think replacing the thermostat would be the logical first thing to try before calling a service technician?
 
  #8  
Old 02-24-13, 02:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,930
Received 262 Votes on 247 Posts
Yes......replacing the thermostat would be the logical first step.
 
  #9  
Old 02-24-13, 04:01 PM
Member
Thread Starter
Join Date: Feb 2013
Location: USA
Posts: 5
Upvotes: 0
Received 0 Votes on 0 Posts
Thumbs up

I have replaced the thermostat and I am happy to report that the furnace is now functioning normally. The draft/exhaust blower is no longer cycling every 3 seconds and heat comes on, runs, and shuts off as it should.

Thanks very much for your time today. Greatly appreciated!

-Joe
Middletown, Delaware

(FYI, new thermostat: basic Honeywell programmable, mod. RTHL2310B1008, $25 from Lowes.)
 
  #10  
Old 02-24-13, 04:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,930
Received 262 Votes on 247 Posts
You are welcome

Those are lower end thermostats but they are easy to program and very reliable.

I like them because I can install them and it doesn't take hours to teach the homeowner to program them.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: