Hot surface ignitor backfed

Hello to all! I am a new member on this site. Received call from Homeowner to troubleshoot furnace. Homeowner disconnected ignitor and used a piece of wire to jumped out plug that ignitor was plugged into, and get gas to stay on to verify ignitor was bad. Owner Indicated hearing a pop. i am an electrician by trade and don't claim to be a furnace expert. I have had some experience troubleshooting though, as I own a couple of rental properties. I tested ignitor with a continuity tester and had no continuity. It seems possible that owner backfed the control board and popped a relay by using the jumper wire thus sending 110 volts back to the board. The board had 24 volts, but i,m not sure if the relay can be replaced, or He just needs a new board. Thanks for any advice.
 
Sponsored Links
  #2  
Old 04-13-13, 06:43 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Welcome tld38.

If a component on a circuit board is fried, the entire board needs to be replaced. To those of us in the HVAC trade, repairing a board is akin to you repairing an AFCI breaker.

FYI:
What the homeowner did by installing that jumper was to create a dead short. The ignitor is fed 120V & when it was powered he had a dead short to the neutral.
 
  #3  
Old 04-13-13, 06:47 PM
Member
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 4,296
Received 2 Votes on 2 Posts
Shorting the wires is obviously a bad move. Check the circuit board for a small, automotive type fuse. If he was lucky, he may have just blown it.

More info on the make and model of the furnace would help.
 
  #4  
Old 04-14-13, 01:03 AM
Member
Thread Starter
Join Date: Apr 2013
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Thanks to all. I have not been back to owners house since yesterday. I had him call the furnace company since they carry many parts. I did test the ignitor and found that that was bad. I think he may have burned out the board by backfeeding it though. I will learn more later. My understanding is that the board is what controls the ignitor to fire, on a call for heat. So in essence, I believe he probably burned out the 24 volt relay that controls 110 volts to the ignitor. I don't know if this fuse would protect in this instance since it usually only protects the ungrounded , or hot side. Thanks again.
 
  #5  
Old 04-14-13, 11:50 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,174
Received 375 Votes on 352 Posts
No....there isn't a fuse on that board that protects it from a short like that.

The relay is vaporized or the relay is welded shut or a foil is burned off the control board.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: