Bryant Evolution Error codes

Reply

  #1  
Old 05-02-13, 07:21 PM
Member
Thread Starter
Join Date: May 2013
Posts: 6
Received 0 Votes on 0 Posts
Bryant Evolution Error codes

I have a Bryant Evolution 355MAV0601 w associated thermostat. With the thermostat I was able to bring up the last 10 error codes. Can you provide any help with what I should check out? Before I list the codes, I'll give some background.
Furnace and AC is a new house build, about 7.5 years old.
I have never had the furnace or AC serviced in the 7.5 years.
About 6 or 8 times in the last 7.5 years, the furnace has shut down without notice, and I've had to go downstairs and disconnect power, and restart it. That always seems to fix it, for weeks or months. This only seems to happen in the winter time, and has never really ever been a serious issue. I have noticed that it seems to struggle to get the fan started, like it is out of balance at lower speeds, but once it gets up to speed it is fine. I don't know if I've ever actually witnessed any of these fault outs, but I can remember sometimes after I reset power, the fan tries to start up, their stops, then it tries to start up again, and stops again, etc.. I honestly cannot remember if this has ever led to a fault that I witnessed, but it just seems like it struggles to get started sometimes.

So these are the error codes:
FN 4/1/2013 9:15 PM 33-LIMIT CIRCUIT FAULT 51 EVENTS
FN 2/4/2013 4:08 AM 13-LIMIT CIRCUIT LOCKOUT 23 EVENTS
FN 1/29/2013 7:22 AM 25-MODEL/SETUP ERROR 89 EVENTS
FN 1/29/2013 5:59 AM 32-LPS OPEN 99 EVENTS
FN 1/29/2013 2:30 AM 45-CONTROL LOCKOUT 41 EVENTS
FN 1/14/2013 1:00 PM 12-BLOWER ON AFTER POWER UP 13 EVENTS
FN 12/8/2011 12:14 AM 23-LPS OR HPS CLOSED 7 EVENTS
FN 12/7/2011 11:55 PM 34- IGNITION FAULT 2 EVENTS
FN 10/24/2009 7:26 AM 42-INDUCER FAULT 3 EVENTS
FN 2/1/2009 5:33 PM 41-BLOWER FAULT EVENTS

Thanks,
Rob
 
Sponsored Links
  #2  
Old 05-02-13, 08:00 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,418
Received 14 Votes on 11 Posts
I recommend having your furnace serviced. The blower motor looks like it is having problems.

Clean the flame sensor, clean the condensate trap, verify that the filter, evaporator coil and secondary heat exchanger are clean, check the blower amperage, check the external static pressure to verify that you do not have an air restriction, inspect the primary and secondary heat exchangers.


http://www.gogeisel.com/geiselonline..._355MAV_OM.pdf

A nest thermostat could not list those past errors.
Looks like you reset the power switch on January 14, 2013.
 
  #3  
Old 05-02-13, 08:12 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,245
Received 2 Votes on 2 Posts
Honestly, I would not try to work on any of the past faults as they are not present and are obviously not faulting constantly. As Houston suggested you should have both furnace and ac units serviced. I recommend either annually or bi-annually.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: