Filling Oil Furnace

Hello, I'm new to this forum but I'm a serious DIY'er.

I'm installing a 50 plate flat plate heat exchanger between my outdoor wood fired boiler (Non-pressurized) and my indoor oil furnace (pressurized). To install the flat plate heat exchanger, I need to drain the oil furnace of the water after it cools off. After making the necessary connections to oil furnace, I will need to fill it again with water. How much pressure must there be on the temperature and pressure gauge for it to operate safely? Thanks in advance for your help. Roger
 
Sponsored Links
  #2  
Old 05-05-13, 06:30 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,077
Received 13 Votes on 11 Posts
A good starting point is 12 psig cold. If your house is taller than average you may need to increase the pressure a bit.
 
  #3  
Old 05-06-13, 11:14 AM
Member
Thread Starter
Join Date: May 2013
Location: USA
Posts: 153
Received 0 Votes on 0 Posts
Grady - Thanks for the reply. After I drained the oil furnace of water, the T&P guage showed 40 psi. I know this is wrong because there was no water in it. I replaced it with a new one and it now reads 12 psi. Again, thanks for your help. Roger
 
  #4  
Old 05-06-13, 11:32 AM
Member
Join Date: Jan 2012
Location: Canada
Posts: 2,739
Received 16 Votes on 15 Posts
As Grady mentioned, 12PSI is a safe level cold.
I tend to run ~20PSI hot. By boiler is in the basement, and the water has to travel 3 stories.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: