Can A/C be added to a coleman Blend-Air furnace?


  #1  
Old 07-03-13, 06:42 PM
L
Member
Thread Starter
Join Date: Jul 2013
Location: usa
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Can A/C be added to a coleman Blend-Air furnace?

Can A/C be added to a coleman Blend-Air furnace?
 
  #2  
Old 07-05-13, 06:24 PM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,606
Received 28 Upvotes on 27 Posts
I'm not familiar with that model. But, an HVAC person may be able to add sufficient ductwork above the furnace bonnet for an A/C evaporator. Or, the evaporator could go elsewhere, maybe in the attic if that is where the main ductwork is..

Personally, I think you'd be better off replacing the furnace with one set up for A/C. Get prices either way.
 
  #3  
Old 07-06-13, 03:44 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,830
Received 57 Upvotes on 50 Posts
Post the model number and blower motor hp rating off the rating plate.

The furnace needs to be able to move enough air for a/c and must have a fan relay. Some of those old furnaces were intended for heating only and have very small blowers.
 
 