AFG oil burner/combustion head


  #1  
Old 09-10-13, 04:55 AM
M
Member
Thread Starter
Join Date: Oct 2003
Location: PA, USA
Posts: 695
Upvotes: 0
Received 0 Upvotes on 0 Posts
AFG oil burner/combustion head

While changing the nozzle on the burner a couple of days ago, I noticed that the head at the end on the air tube had developed a few heat cracks and fractures. No big deal, thought I'd just replace it. Picked up a new one, same as the old one - F6. But looking at the card that came with it, I see that Beckett recommends an F6 head for a burner that puts out 0.85 to 1.65 gph. My furnace has always been set up for a .65/80B nozzle.. Beckett states F0 as the correct head for the .65 firing rate So what's an F6 head doing there?? Should I scrap the F6 and try the F0? I should add that the furnace is about 10 years old and I've been pretty happy with way it runs. All these heads look the same to me, but maybe I just don't know any better.. Thanks in advance for any advice.
 
  #2  
Old 09-10-13, 05:36 AM
T
Member
Join Date: Jun 2012
Posts: 955
Received 31 Upvotes on 25 Posts
The F6 should have been changed when it was initially set up to fire @ .65.
You will need a combustion analyzer to reset the CO correctly with the new head.
 
  #3  
Old 09-13-13, 04:02 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
What is the make & model of the furnace? Given that information, I can probably find out the correct burner head & nozzle.
 
  #4  
Old 09-14-13, 03:39 AM
M
Member
Thread Starter
Join Date: Oct 2003
Location: PA, USA
Posts: 695
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks, Grady. I already called up Beckett and they informed me that for the type of furnace I have and the oil pressure at the nozzle, F6 is the correct head to have on the burner.

Sorry for the false alarm.
 
  #5  
Old 09-14-13, 04:24 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Like you, I thought the F6 was big for a .65 nozzle. The only furnace I know of off the top of my head that uses a .65 x 80*B nozzle is a Armstrong (Ducane) & the pump pressure is 140#.
 
 