Need Help Finding Correct Blower Motor To Install
#1
Member
Thread Starter
Join Date: Sep 2013
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Need Help Finding Correct Blower Motor To Install
I just moved into this house about 2 months ago, so I don't know a whole lot about the heating/cooling system. I have a very old Bryant 353 type 140 Oil Fired Air Furnace, which looks like it was installed in the 70's. I need to eventually replace it, but i don't have a few grand to do that right now. I think it's a direct drive (there was no belt when I removed the blower motor).
My issue is the blower motor died a few weeks ago. I concluded this due to the breaker suddenly tripping, then tripping the second I turn the breaker back on. I'm thinking I have a blower issue, capacitor issue or board issue. I'm replacing the blower/capacitor to hopefully fix the issue. Fingers crossed it's not the board.
Today I pulled out the blower motor to find that there are no specs on the motor itself - so I'm clueless as to what motor I need to buy to replace it with. I pulled the motor totally out and absolutely no markings, numbers or specs. The furnace itself is from the 70's, and was installed as heating only. In 1999 it looks like a cooling system (evaporator coil) was retrofitted to the system. It's an Lennox and the plate showing the model number, etc appears to be gone (I can see where it used to be)
Any help would be really appreciated, as I live in PA and heating is going to be a big deal in the next few weeks. I have included some images here that may be useful to helping me identify the blower part number, including pictures of the furnace manual.
Furnace Data Plate:
http://i.imgur.com/NONC3L3h.jpg
Burner:
http://i.imgur.com/Q299J3Nh.jpg
Wires Going To Blower Motor:
http://i.imgur.com/PZ9AjWsh.jpg
Furnace Manual Front Page:
http://i.imgur.com/TyIgtnSh.jpg
Furnace Manual Blower Motor Page:
http://i.imgur.com/GBW0YiSh.jpg
Thanks for taking the time to read this!
My issue is the blower motor died a few weeks ago. I concluded this due to the breaker suddenly tripping, then tripping the second I turn the breaker back on. I'm thinking I have a blower issue, capacitor issue or board issue. I'm replacing the blower/capacitor to hopefully fix the issue. Fingers crossed it's not the board.
Today I pulled out the blower motor to find that there are no specs on the motor itself - so I'm clueless as to what motor I need to buy to replace it with. I pulled the motor totally out and absolutely no markings, numbers or specs. The furnace itself is from the 70's, and was installed as heating only. In 1999 it looks like a cooling system (evaporator coil) was retrofitted to the system. It's an Lennox and the plate showing the model number, etc appears to be gone (I can see where it used to be)
Any help would be really appreciated, as I live in PA and heating is going to be a big deal in the next few weeks. I have included some images here that may be useful to helping me identify the blower part number, including pictures of the furnace manual.
Furnace Data Plate:
http://i.imgur.com/NONC3L3h.jpg
Burner:
http://i.imgur.com/Q299J3Nh.jpg
Wires Going To Blower Motor:
http://i.imgur.com/PZ9AjWsh.jpg
Furnace Manual Front Page:
http://i.imgur.com/TyIgtnSh.jpg
Furnace Manual Blower Motor Page:
http://i.imgur.com/GBW0YiSh.jpg
Thanks for taking the time to read this!
#2
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Yours is a direct drive. In that case, you would need a 1/3 HP motor. The number & colors of the wires indicate the original was a 4 speed but a 3 speed would work & likely be more available & cheaper. Most likely it is a 1/2" diameter shaft but measure to be sure.
BTW, with that vintage furnace there is no board.
BTW, with that vintage furnace there is no board.
#3
Member
Thread Starter
Join Date: Sep 2013
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the reply!
Any idea on the voltage? It looks like 115v is the common motor, but I don't see a voltage rating anywhere.
If 115V I'm thinking this would this be a good fit:
MOT6001B - Universal 1/3 HP 115v 4-Speed 1075 RPM Blower Motor MOT6001B
Edit: Yes it's a 1/2" shaft, and the motor itself has a 5.5" diameter
Any idea on the voltage? It looks like 115v is the common motor, but I don't see a voltage rating anywhere.
If 115V I'm thinking this would this be a good fit:
MOT6001B - Universal 1/3 HP 115v 4-Speed 1075 RPM Blower Motor MOT6001B
Edit: Yes it's a 1/2" shaft, and the motor itself has a 5.5" diameter
#5
Member
How were you planning on replacing the motor? If you were going to buy one from a local HVAC supply place, you might as well take it, or even some pictures of it, there and ask them for a replacement.
You might also talk to some of the pros at the place, you might be able to negotiate a deal with one of them. I regularly find that the pros at building supply places are very helpful at explaining why I really should not try whatever it is I am planning.
You might also talk to some of the pros at the place, you might be able to negotiate a deal with one of them. I regularly find that the pros at building supply places are very helpful at explaining why I really should not try whatever it is I am planning.