york furnace 8 red flashes


  #1  
Old 09-19-13, 11:32 AM
B
Member
Thread Starter
Join Date: Sep 2013
Location: canada
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
york furnace 8 red flashes

I have a York PS8B12N100UH11B - burners supply heat for 5 cycles - then system shuts down - showing 8 red flashes. Diagnostic fault code indicates "ignition lockout due to recycles" . System will shut off for about an hour and then start up again and the problem repeats. Manual states "low gas pressure or faulty gas valve" - any repair advice would be appreciated!!
Thank you
 
  #2  
Old 09-19-13, 12:44 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,100
Received 3,982 Upvotes on 3,574 Posts
Welcome to the forums.


Is your furnace running on propane ?

Is so.....have you checked the tank pressure.....could the tank be low ?

Visually check the flame to see how it looks also.

If you believe the propane system is ok then I would try cleaning the flame sensor rod first. The flame sensor is a single rod that sits in the flame. You remove it's one screw and clean the rod with a scotch pad or steel wool. Make it nice and shiny.
 
 