Bryant blower cuts on and off

Hi all,

I'm hoping someone can help me with this:

I have a Bryant (Plus 90) 350MAV furnace and I recently noticed it seemed to be short cycling. Upon closer inspection I've found that it is actually the blower turning on and off after the burner shuts off. Sometimes the blower will start and then cut off instantly, sometimes it will run from a few seconds to about a minute.
It repeats this for a while, followed by a few minutes of silence before it does it again a few times randomly. The blower seems to run fine / steadily while the burner's on, however.

I've turned shut off the power to the furnace and turned it on again, get a 12 error code, and then the LED stays a solid red with no other flashes.


Does anyone know what could be causing this?
I've done some research but have yet to come across anything that close enough to try. The closest I can get to a possible cause seems to be maybe a faulty blower relay. A lot of similar sounding cases had different fixes so I'm not completely certain.

Thanks in advance, I really hope someone here can tell me what's causing this.
Will provide more info if needed.
 

Last edited by Andromyde; 10-11-13 at 01:33 AM.
  #2  
Old 10-11-13, 05:15 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
>


Erratic operation of the fan as you describe is probably a defective circuit board that needs to be replaced.
 
  #3  
Old 10-11-13, 06:35 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
Here is a link to a guide for your unit that lists the error codes on pages 11 and 12:

http://www.gogeisel.com/geiselonline..._355MAV_OM.pdf
 
  #4  
Old 10-11-13, 08:28 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,590
Received 3,880 Upvotes on 3,477 Posts
Welcome to the forums.

Erratic operation of the fan as you describe is probably a defective circuit board that needs to be replaced.
Since the blower motor relies on timing from the control board to operate.... I second that diagnosis.
 
  #5  
Old 10-11-13, 08:51 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
Blower control lockout is the error code shown in the manual I linked. I found some in-depth steps to take to troubleshoot fault code 12: ftp://ftp.mingledorffs.com/Tech_Serv..._1993-2002.pdf

The first step is to turn off the circuit breaker for the furnace, wait 30 seconds and turn breaker back on. Then set thermostat to heat. Hopefully, that will clear the issue. If not you will need a multimeter to test voltages.
 
 