Trane XE80 is not generating any heat - control board gives 3 flashes
#1
Member
Thread Starter
Join Date: Oct 2013
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Trane XE80 is not generating any heat - control board gives 3 flashes
Trane XE80 3 flashes
The problem is that the unit doesn't try to do anything in heat mode, there's a series of clicks and then the red led flashes 10 times then 3 times over and over again. According to the chart, that means the the pressure switch sees an error.
However, no fan, no inducing fan, no fire... nothing.
Whats already done so far
-
1. I tried to turn on the fan from my thermostat directly, it is turning on but not in auto and heat mode.
2. Everything is running fine in Auto and Cold mode.
3. I have changed the ignition switch that did not help.
4. I have changed the pressure switch that did not help.
5. Cleaned the white hose that goes into the pressure switch.
6. Cleaned the flame sensor.
I'm getting temptive to try replacing the control board with the other furnance to see if this fixes the issue.
Please help-
PS: I have separate furnance for 1st and 2nd floor so that's why end up swaping the ignition switch and pressure switch.
Thanks & Regards,
Sandeep Sood
The problem is that the unit doesn't try to do anything in heat mode, there's a series of clicks and then the red led flashes 10 times then 3 times over and over again. According to the chart, that means the the pressure switch sees an error.
However, no fan, no inducing fan, no fire... nothing.
Whats already done so far

1. I tried to turn on the fan from my thermostat directly, it is turning on but not in auto and heat mode.
2. Everything is running fine in Auto and Cold mode.
3. I have changed the ignition switch that did not help.
4. I have changed the pressure switch that did not help.
5. Cleaned the white hose that goes into the pressure switch.
6. Cleaned the flame sensor.
I'm getting temptive to try replacing the control board with the other furnance to see if this fixes the issue.
Please help-
PS: I have separate furnance for 1st and 2nd floor so that's why end up swaping the ignition switch and pressure switch.
Thanks & Regards,
Sandeep Sood
Last edited by talk2sood; 10-12-13 at 10:18 AM.
#2
Welcome to the forums.
The pressure switch sees an error because the draft inducer fan isn't running. When there's a call for heat.....that inducer needs to start first before anything else.
You need to determine if the motor is defective or it's not getting power. You can use a voltmeter and check the motor leads for 120vac after setting the thermostat to call for heat.
If there is power to the motor then then it is defective.
If there is no power then the control board is most likely the problem.
The pressure switch sees an error because the draft inducer fan isn't running. When there's a call for heat.....that inducer needs to start first before anything else.
You need to determine if the motor is defective or it's not getting power. You can use a voltmeter and check the motor leads for 120vac after setting the thermostat to call for heat.
If there is power to the motor then then it is defective.
If there is no power then the control board is most likely the problem.
#3
Member
Thread Starter
Join Date: Oct 2013
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you for a tip.
May I request you to tell me how to determine if motor is defective via voltmeter? i.e. which terminals to connect by voltmeter.
I have attached a picture of control board for your information purpose.
Thanks again.
Regards,
Sandeep Sood
May I request you to tell me how to determine if motor is defective via voltmeter? i.e. which terminals to connect by voltmeter.
I have attached a picture of control board for your information purpose.
Thanks again.
Regards,
Sandeep Sood
#5
When the thermostat calls for heat it should energize the W terminal with 24 VAC. When that terminal is properly energized, the circuit board should switch on 120 VAC to power up the inducer motor.
So...
Check to see if the W terminal is being energized. If it is, then check to see if you have 120 VAC across the two wires to power the inducer motor.
If you DO have 120 VAC to the inducer motor and the motor doesn't start and run, you have a bad inducer motor.
If the W terminal is energized and there is no voltage switched on to power the inducer motor, you probably have a defective circuit board that needs to be replaced.
So...
Check to see if the W terminal is being energized. If it is, then check to see if you have 120 VAC across the two wires to power the inducer motor.
If you DO have 120 VAC to the inducer motor and the motor doesn't start and run, you have a bad inducer motor.
If the W terminal is energized and there is no voltage switched on to power the inducer motor, you probably have a defective circuit board that needs to be replaced.
#8
Member
Join Date: Jan 2014
Location: usa
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Trane XV95 Problem - No heat
I'm new to this site and I'm not sure how to post a new problem. My furnace draft motor kicks on and increases speeds and shuts off with out any attempts for iginition. Only 26 mths old. Continues to do this every 2 minutes. Any ideas?
#9
Member
Join Date: Apr 2011
Location: nj
Posts: 526
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Pj is probably going to move this to its own thread, but either the inducer isn't properly pulling the correct draft, the tubing is clogged, the pressure switch is bad (rarely ever the case) or it could just be the hot surface ignitor is cracked.how long after the inducer starts running does it shut off? A minute? Or seconds?
#10
Member
Join Date: Jan 2014
Location: usa
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
After 20 seconds the inducer shuts off. We had a light, dry snow last night and I went outside to check the vent pipes. THe exhaust had a one foot tall stalagtite forming from the ground while the intake had a ice/snow film covering the vent screen. Once I cleaned the intake scrren off the furnanced fired right up. Thanks for the advice.