Question A/C, Fan , Gas Furance not turning on. Help Plz

My AC, Fan, and Furance won't turn on.
Things I have replaced are
Control Board with exact same model
Safety switch for door
Transformer for unit

Things I have checked
I have 120v into transformer and 24v coming out
No lights on control board
I tried jumping wires at thermostat R to G, R to Y, R to W nothing happens
3 amp fuse on control board isn't blown
Breaker on the outside is not tripped(I turned off and on to reset)

Please help I don't know where to go from here
 
  #2  
Old 10-19-13, 12:51 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,730
Received 4,115 Upvotes on 3,695 Posts
Welcome to the forums.

On the board should be 24vac input. Did you check for power there ?

If it's at the transformer...... it should be at the board.
 
  #3  
Old 10-19-13, 12:54 PM
R
Member
Thread Starter
Join Date: Oct 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
How do I check for power at the board?
 
  #4  
Old 10-19-13, 12:58 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,530
Received 95 Upvotes on 88 Posts
Measure for 24VAC between R and C.

Post the make and model number of the furnace so we can see what we are working on.
 
  #5  
Old 10-19-13, 01:07 PM
R
Member
Thread Starter
Join Date: Oct 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also thank you for welcoming me.

Yes I have 24vac at board.

its a GMP100-3 Rev A
Control board is Goodman B18099-13 1012-933A
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: