Day & Night Gas Furnace turns on and off twice after completing heating cycle
I have a Day & Night gas furnace. It heats the house fine but after a heating cycle is complete and the fan shuts off, the fan will start up for a second then shut down and a couple seconds later it will do it again. This seems to be more of an irritation than anything but could this be a warning of future problems?
I tried changing batteries in the thermostat and the limit switch with no change in operation.
Any ideas?
I tried changing batteries in the thermostat and the limit switch with no change in operation.
Any ideas?
#2
Welcome to the forums.
That's not an un-common problem. It happens when there is extra heat left in the heat exchanger.
It's not controlled by the thermostat but by a limit switch.
You mention limit switch.... is it an adjustable one for the blower ?
That's not an un-common problem. It happens when there is extra heat left in the heat exchanger.
It's not controlled by the thermostat but by a limit switch.
You mention limit switch.... is it an adjustable one for the blower ?
#3
Member
Thread Starter
Join Date: Dec 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the reply PJ.
The switch I changed is installed just above the burner inside the heat exchanger. It’s a non-adjustable 180 – 140 degree switch, it turns on the fan at 180 and shuts it off at 140.
The switch I changed is installed just above the burner inside the heat exchanger. It’s a non-adjustable 180 – 140 degree switch, it turns on the fan at 180 and shuts it off at 140.
#4
PJmax meant to say fan switch. Sounds like you changed the limit. If this old enough to have a fan switch and not a fan timer board, I believe it probably has a Camstat fan switch. Look for it close to the limit. If it does have this it will have a red face as I recall and it is adjustable. However those were known to short cycle after they became old. This happens mostly on counterflo models
#5
His unit doesn't have an adjustable fan control. It's a preset control that looks like a limit switch (clixon)
#6
Member
Thread Starter
Join Date: Dec 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The only fan control I've noticed beyond the limit switch is a terminal board used to adjust the fan speed. A sticker on the lower access panel mentions three speeds and moving a wire accomplishes this task.