Day & Night Gas Furnace turns on and off twice after completing heating cycle

I have a Day & Night gas furnace. It heats the house fine but after a heating cycle is complete and the fan shuts off, the fan will start up for a second then shut down and a couple seconds later it will do it again. This seems to be more of an irritation than anything but could this be a warning of future problems?

I tried changing batteries in the thermostat and the limit switch with no change in operation.

Any ideas?
 
  #2  
Old 12-08-13, 09:09 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,952 Upvotes on 3,545 Posts
Welcome to the forums.

That's not an un-common problem. It happens when there is extra heat left in the heat exchanger.
It's not controlled by the thermostat but by a limit switch.

You mention limit switch.... is it an adjustable one for the blower ?
 
  #3  
Old 12-08-13, 09:17 AM
J
Member
Thread Starter
Join Date: Dec 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the reply PJ.

The switch I changed is installed just above the burner inside the heat exchanger. It’s a non-adjustable 180 – 140 degree switch, it turns on the fan at 180 and shuts it off at 140.
 
  #4  
Old 12-08-13, 12:50 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,277
Upvotes: 0
Received 3 Upvotes on 3 Posts
PJmax meant to say fan switch. Sounds like you changed the limit. If this old enough to have a fan switch and not a fan timer board, I believe it probably has a Camstat fan switch. Look for it close to the limit. If it does have this it will have a red face as I recall and it is adjustable. However those were known to short cycle after they became old. This happens mostly on counterflo models
 
  #5  
Old 12-08-13, 12:53 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,952 Upvotes on 3,545 Posts
His unit doesn't have an adjustable fan control. It's a preset control that looks like a limit switch (clixon)
 
  #6  
Old 12-08-13, 02:01 PM
J
Member
Thread Starter
Join Date: Dec 2013
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
The only fan control I've noticed beyond the limit switch is a terminal board used to adjust the fan speed. A sticker on the lower access panel mentions three speeds and moving a wire accomplishes this task.
 
 