Honeywell zone valves

I have two zones for heat both have Honeywell zone valves. When I turn my thermostats to call for heat neither valve is working? Any help is appreciated
 
  #2  
Old 01-05-14, 08:13 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,183
Received 77 Votes on 69 Posts
Sounds like the transformer went bad.... Test the transformer that powers the zone valves and see if there is 24v at the terminals...
 
  #3  
Old 01-06-14, 08:52 AM
T
Member
Thread Starter
Join Date: Jan 2014
Posts: 2
Received 0 Votes on 0 Posts
Thank you Lawrosa that was it appreciate your help. That's one problem solved. You know anything about wood furnaces?
 
 