It's -38 here in northern Ohio! I have a older Bryant furnace (40 years old or so) I can get the pilot lit, then I turn on the gas valve to on, and turn on the power to the furnace, the furnace will light the burners but after a few seconds I hear a pop in the control valve and the gas is shut off and everything goes out including the pilot. Now I did have to have the control valve replaced a couple years ago, it has a dual valve standing pilot control valve in it. Hope someone has an idea .. THANKS!
#2
Welcome to the forums.
Is that a millivolt system ? No 24vac transformer. Two wires to the thermostat ?
A weak pilot generator or a defective themocouple if it's not a millivolt system.
Is that a millivolt system ? No 24vac transformer. Two wires to the thermostat ?
A weak pilot generator or a defective themocouple if it's not a millivolt system.
#4
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes pilot stays lit, turn the valve to on and it continues to stay lit. I then turn the power switch on the side of the furnace on and the burners all light, however after about 5 seconds? I hear the pop come from the control valve and all gas is shut off and everything goes out , however the fan keeps running.
I'm not sure what your talking about as far as millivolt system goes, i think I'm looking at the thermostat it says "cam-stat" on it and "fixed limit 190F . It has 3 wires coming from it. also the switch on the side looks like a big transformer of some kind about the size of a baseball.
thank you guys so much
I'm not sure what your talking about as far as millivolt system goes, i think I'm looking at the thermostat it says "cam-stat" on it and "fixed limit 190F . It has 3 wires coming from it. also the switch on the side looks like a big transformer of some kind about the size of a baseball.
thank you guys so much
#6
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
don't think so, sometimes the fan doesn't come on yet when the burners light. I messed with it for a few hours tonight. Don't think fan has any effect on when the gas goes out though
#7
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 40 Upvotes
on
38 Posts
This is somewhat of a long shot but maybe the pilot orifice is dirty or slightly clogged. I suggest you remove the pilot assembly, brush with a fine wire brush, & flush with solvent such as carb cleaner then blow it out well. Put it back together & give it a go.
#10
It may be that it was dirty which can affect operation. A new one is about $10-15 and you can clean the old one with an abrasive pad, like a green meanie. I don't think they recommend steel wool or sandpaper...not sure.
Glad you have heat. I knew there was a reason I moved away from Ohio and never looked back. -38F? Good grief!
Glad you have heat. I knew there was a reason I moved away from Ohio and never looked back. -38F? Good grief!
#11
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
yeah i picked one up today for 11 dollars, gonna switch it out when it warms up a little bit. This is the coldest i can ever remember around here. It's -3 right now with out windchill!
#12
Please get that thing checked out. Just because it's running now doesn't mean it's safe - you might need a new furnace, not a thermocouple.
30-40% of the heat you're paying for is going right up the chimney whether it's safe or not.
30-40% of the heat you're paying for is going right up the chimney whether it's safe or not.