I have a Frasier PBNU-LD10N060D that is used just to heat the basement. I use it only about a dozen days a year. The venter motor went out so I replaced it. Everything worked for a few days. Then I started having problems again. The venter motor comes on, the ignitor glowed for a few seconds, the burner came on for just a couple of seconds, then everything shut down. This cycle repeated every minute. I decided to replace the control box. Now the venter comes on but just keeps running and nothing else happens. The ignitor does not glow. I checked my outside intake and exhaust pipes and there feels like there is plenty of air movement. I can't believe it's the control box but I don't know. Any suggestions?
#2
Welcome to the forums.
Did you reconnect the tube from the venter to the pressure switch ?
Have you confirmed with a meter that the pressure switch closes when the venter starts ?
Did your old board have a blinking LED on it ?
Can't find any info on your York/Luxaire/Frasier/Johnson furnace.
Did you reconnect the tube from the venter to the pressure switch ?
Have you confirmed with a meter that the pressure switch closes when the venter starts ?
Did your old board have a blinking LED on it ?
Can't find any info on your York/Luxaire/Frasier/Johnson furnace.
#3
Member
Join Date: Apr 2011
Location: nj
Posts: 526
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Most times when the flame comes on for a split second then shuts off, it's the flame sensor. You didn't toss away your old control did you? I would put that one back on, clean the sensor and retest.
#4
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the replies.
The flame does not come on at all. I did clean the sensor anyway.
The old controller had a solid red LED stay on. That's why I thought it was bad. The new contoller does not have the LED come on at all.
I did reconnect all the hoses to the venter. The pressure switch does not close when the venter comes on. I took the hose off and sucked into it, I hear a click and after about a minute the igniter comes on but not the burner. What does this mean?
Thanks again.
The flame does not come on at all. I did clean the sensor anyway.
The old controller had a solid red LED stay on. That's why I thought it was bad. The new contoller does not have the LED come on at all.
I did reconnect all the hoses to the venter. The pressure switch does not close when the venter comes on. I took the hose off and sucked into it, I hear a click and after about a minute the igniter comes on but not the burner. What does this mean?
Thanks again.
#5
Member
Join Date: Apr 2011
Location: nj
Posts: 526
Upvotes: 0
Received 0 Upvotes
on
0 Posts
That means your fan is probably not doing what it's supposed to do. Did you put back an exact Manufacturer replacement part or did you use a universal motor? Inducer motors are not recommended to be replaced with anything other than the manufacturer's replacement part.
#6
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I did use the exact manufacturer's replacement motor. This furnace is just used for the basement. I have another Frasier furnace like this only bigger for the upstairs. About all the parts are identical between the two furnaces. I put the upstairs furnace venter in the basement furnace. There were no changes in doing this. So I think the replacement venter is good.
#12
Member
Thread Starter
Join Date: Jan 2014
Location: usa
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I think I'm getting somewhere. But I'm not sure what to do. I noticed that the LED on the controller for the main furnace blinks once at the beginning of a cycle. Then it stays off for the whole cycle. The LED on the basement controller never comes on. There's a test connector with 9 pins on it. Three of the pins, according to the attached schematic say they should be 24V. The other six pins should be 115V. Only pins 1 and 7 are 24V when the furnace comes on. And pins 6 and 9 arte 115V. All other pins are zero volts. Does this point to the transformer?
#13
If you are finding 24vac on the board then the transformer is good. I can't help you much after that since I can't see the schematic (too small) and could not find an online manual for your unit.