Rudd Heating Unit
Old 03-28-14, 07:59 AM
1
Rudd Heating Unit
I have a Rudd Achiever Super Quit 80. When the unit turns on the exhaust fan comes on, the electric igniter comes on, then the flame comes on, then goes out. I'm thinking the thermo coupling is out. Is there any way of checking it? Or any other ideas? Also the lights on the circuit board stay green. So no codes.
Old 03-28-14, 09:24 AM
G
Received 2 Upvotes on 2 Posts
Your description sounds like a classic flame sensor problem. Locate the flame sensor and gently clean it with fine steel wool, a dry SOS pad, or similar. You just want to clean it up, not remove metal.
I almost forgot - welcome to the forums.
1956mike voted this post useful.
Old 03-28-14, 09:50 AM
1
Ok thanks, Did that and it still shuts back off. So do I replace the flame sensor?
Old 03-28-14, 10:21 AM
R
Any cracks in the porcelain part of the flame sensor? The should pass about 2-4 microAMPS when cleaned. Unless you have a meter that can do that, you can't test the flame sensor. Check for a break in the wire back to the controller as well, loose connection and so on.