Carrier Weathermaker 8000 Ignition Problem
Old 04-23-14, 06:14 PM
Hi
we have a Carrier Weathermaker 8000 Ignition Problem with a code 34. we replaced the ignitor and its still not glowing.
There are what should is the sequence:-
1. Main blower comes on for 90 sec
2. Inducer motor comes on for 20 sec
3. Heating element turns does not turn on
at this point I am not sure what else to look at to help diagnose the issue.
any suggestions would be appreciated.
Thank you.
Old 04-24-14, 05:39 PM
user 10's Avatar
The error codes should be listed on the schematic. (on blower compartment access panel)
The most likely errors in your case are...
1. Pressure switch stuck open -> venting issue, badly cracked heat exchanger, bad pressure switch (don't change the pressure switch, it's unlikely to be bad)
2. Flame not sensed -> in this case, you have to see if the igniter is getting power when it should. Do you have a volt meter and know how to use it?
Old 04-24-14, 05:44 PM
user 10's Avatar
re: main blower comes on for 90 sec - has it always done this?
Old 04-24-14, 07:47 PM
Carrier will run the blower motor for 90 seconds on power up if there is a call for heat.