Bryant 310AAV draft inducer motor constantly running

Reply

  #1  
Old 07-07-14, 09:08 AM
Member
Thread Starter
Join Date: Aug 2006
Posts: 1
Received 0 Votes on 0 Posts
Bryant 310AAV draft inducer motor constantly running

I noticed that my draft inducer motor is constantly running on Bryant 310AAV.

Tstat is in cooling mode, so no call for heat.

Remove t-stat completely same issue.

As soon as furnace powered inducer motor comes on, blower is off.

No error code displayed by LED. Temporary I removed power to the inducer motor.

Appreciate feedback, or how to troubleshoot the issue.

B
 
Sponsored Links
  #2  
Old 07-07-14, 11:14 AM
Member
Join Date: Sep 2008
Location: Long Island
Posts: 769
Received 0 Votes on 0 Posts
relay on control module is welded shut remove white wire off board to verify your not getting 24s to coil for said relay...slight tap with screwdriver on boxed relays on board might break it loose..
 
  #3  
Old 07-07-14, 11:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,608
Received 339 Votes on 317 Posts
Welcome to the forums.

As soon as furnace powered inducer motor comes on, blower is off.
I don't understand what that means.
 
  #4  
Old 07-13-14, 12:11 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,372
Received 10 Votes on 8 Posts
Sounds like a faulty furnace control board. remove the W wire as Sminker has posted to prove this but I have had to replace boards for this in the past.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: