carrier weathermaker code 32
I have a carrier weathermaker model 58tma10016 with control board hk42fz005. I get a code 32 due to the inducer not starting. All switches checked and working. I get 24vac with t-stat asks for heat. Initially I don't hear the inducer relay kick in but after a power reset the relay will come on intermittently and the inducer motor will run for a short time while the relay is energized. After many safety circuit resets the relay finally activates and the inducer motor runs then code 32 clears and I get heat. I don't think the problem is any of the sensors but I'm focusing on the main board as the culprit. I am looking at replacing the board with a carrier board 325879-751 or finding someone who can repair my old board hk42fz005. Any suggestions greatly appreciated. Thanks
#3
Member
Thread Starter
Join Date: Oct 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
All vents have been checked and are clear. No blockages anywhere and replaced tubing to pressure switches. I also want to add that the reason I shut off the t-stat is that the furnace is in my garage and I turn it off when I leave.
#4
Welcome to the forums.
It does sound like a control board problem. However... I would put a voltmeter on the inducer motor leads to confirm that you do have a loss of 120vac and that it is not a motor problem.
I don't think you'll find anyone to service your old board. Too much of a liability.
It does sound like a control board problem. However... I would put a voltmeter on the inducer motor leads to confirm that you do have a loss of 120vac and that it is not a motor problem.
I don't think you'll find anyone to service your old board. Too much of a liability.
#5
Member
Thread Starter
Join Date: Oct 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
No loss to inducer motor. Got 120vac and as we speak furnace is running. There are 2 relays involved IDR and IHI/LOR. The first one is the spst inducer motor which is normally open and the second relay is the inducer speed change relay spdt for hi/lo operation. I can hear one of them try to engage but then drop out immediately. That's the time I do my multiple reset and that relay finally stays on. I can hear a high pitched sound as the relay tries to activate.
#6
No loss to inducer motor.
Yes....you are going to have 120v on the motor when it's running but you need the check that voltage when the motor is not running.
#7
Member
Thread Starter
Join Date: Oct 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Just checked the leads to the inducer. When furnace finishes cycle no 120vac present at the motor leads. How do I check 120vac going to the relay without removing the board. Thanks