I understand the vent of a high effiency furnace is supposed to slope back toward the furnace so condensate runs back to the furnace.

However, is the air intake also supposed to slope back toward the furnace the same way?
 
  #2  
Old 10-16-14, 06:09 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,644
Received 72 Upvotes on 65 Posts
If you have a 2 pipe application, yes both should slope back to the furnace.

Refer to the installation manual of your furnace.
 
 