Noisy Cold Air Return (only one in the house)
#1
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Noisy Cold Air Return (only one in the house)
Hi all,
Just bought a 1200 sq ft 1962 Rambler south of Seattle, WA a month ago. Kicked on the brand new 92% Payne forced air furnace last week and was surprised by how loud the sole return air register is. The furnace is located in a bedroom closet (down-flow position), as there is only a crawl space. The return air register is in the hallway right outside the furnace (this is not a central location of the house) near the ceiling.
I had an HVAC mechanic stop by to check it out, figuring I will need to add more returns, but he just advised moving the return to the central living room/kitchen area (above the hallway entrance in photo 3) with flexible duct through the attic space. Seemed like a good suggestion to reduce the noise. He indicated having only one return was normal.
Then I started researching airflow and circulation and have hit a bunch of contradictory info leaving me confused about the best course of action. Some sources say you should have cold air returns in every room for the most efficient heating, others seem to indicate having only one return is fine? Some say the returns should be near the floor (makes sense), others seem to install near the ceiling? Then there's undercutting the doors or adding grates to them so when they are closed at night you still get proper circulation?
Any thoughts would be greatly appreciated. I have replaced a few furnaces in my day and run duct work, but never had a great idea of the proper layouts for maximizing efficiency. Thanks!


Just bought a 1200 sq ft 1962 Rambler south of Seattle, WA a month ago. Kicked on the brand new 92% Payne forced air furnace last week and was surprised by how loud the sole return air register is. The furnace is located in a bedroom closet (down-flow position), as there is only a crawl space. The return air register is in the hallway right outside the furnace (this is not a central location of the house) near the ceiling.
I had an HVAC mechanic stop by to check it out, figuring I will need to add more returns, but he just advised moving the return to the central living room/kitchen area (above the hallway entrance in photo 3) with flexible duct through the attic space. Seemed like a good suggestion to reduce the noise. He indicated having only one return was normal.
Then I started researching airflow and circulation and have hit a bunch of contradictory info leaving me confused about the best course of action. Some sources say you should have cold air returns in every room for the most efficient heating, others seem to indicate having only one return is fine? Some say the returns should be near the floor (makes sense), others seem to install near the ceiling? Then there's undercutting the doors or adding grates to them so when they are closed at night you still get proper circulation?
Any thoughts would be greatly appreciated. I have replaced a few furnaces in my day and run duct work, but never had a great idea of the proper layouts for maximizing efficiency. Thanks!



#2
Group Moderator
I lived in a place with only one return like that and everything worked pretty well. That said, it was just my girlfriend and me so doors were rarely shut inside so I don't know if we would have had issues with doors being closed for extended periods.
You have vents in each room, right?
How is the temperature in the house in the different areas?
You have vents in each room, right?
How is the temperature in the house in the different areas?
#4
Group Moderator
I'd live with it a little while and see how it works.
What is the noise - rattle of the duct, air turbulence, ...?
What is the noise - rattle of the duct, air turbulence, ...?
#5
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Air turbulence. Not something we're going to be able to live with, it's really loud and right next to our bedroom. Sounds like a plane is taking off inside the house.
#7
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the advice. Think I'll move the return as suggested and install something like this in the bedrooms: Tamarack TTi-RAPR12.4 Return Air Pathway RAP - Tamarack Ventilation System
#8
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
I'd much rather see a real return system. You could put a return in the ceiling of each room & install flex back to the return plenum. Easy, inexpensive, & most importantly, will work WAY better.
#12
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
The noise is most likely due to high velocity in the return air grille. Adding return air ducts as suggested by Grady IS a definite improvement. You might try simply removing the grille to see if it makes a significant difference in the noise level and then either replacing it with a grille with much less restriction or trying to straighten the louvers on the existing grille with pliers as a temporary stop-gap measure.
Newer furnaces have higher velocities in their airflow and that will often make a new furnace in an older ductwork system noisy. You MIGHT be able to slow down the blower but you would need to also measure the temperature differential across the heat exchanger so this might be a job for a QUALIFIED technician. Unfortunately, finding a competent technician may be difficult.
Newer furnaces have higher velocities in their airflow and that will often make a new furnace in an older ductwork system noisy. You MIGHT be able to slow down the blower but you would need to also measure the temperature differential across the heat exchanger so this might be a job for a QUALIFIED technician. Unfortunately, finding a competent technician may be difficult.
#13
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Sorry for the slow reply. I've been out of town for a few days.
For the 120 sq. ft. room I'd use a 7" return & a 6" for the 90 sq. ft. room. An 8" common would be a little small, so I'd suggest a 10" since 9" duct is hard to find.
For the 120 sq. ft. room I'd use a 7" return & a 6" for the 90 sq. ft. room. An 8" common would be a little small, so I'd suggest a 10" since 9" duct is hard to find.