York Furnace Shut Down with Pressure Switch Lockout code

I have a York Model TG95080 gas furnace that was installed four years ago. It works most of the time but occasionally will not start due to a Pressure Switch Lockout code. This seems to occur in the early and late season and maybe when the humidity is high. If I recycle the power a couple of times, I have always been able to get the furnace to work again (and it will continue to work).
The furnace has always done this and the installer has replaced a few parts and added a water trap on the exhaust pipe (the water trap is required as per the manual).

The manual specifies a maximum of 65' for 2" vent pipes but my measurements indicate a length of 81.75' (34.25' pipe plus eight 90deg long sweep elbows plus three 45deg elbows).

I suspect the extra vent pipe length is the cause. Is there a way to prove this is the problem? And thus, maybe convince the installer that this is his problem?
 
Sponsored Links
  #2  
Old 10-25-14, 11:42 AM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Received 0 Votes on 0 Posts
WOW, he didn't install the condensate trap? Yes there is a way test it, but I wouldn't consider it a DIY job. Call him back till he figures it out. I would pull the combustion blower out and inspect it.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: