No heat, Trane xe 80, already ruled things out, very confused, please help!!

No heat, Trane xe 80, already ruled things out, very confused, please help!!

Reply

  #1  
Old 11-04-14, 08:40 AM
Member
Thread Starter
Join Date: Nov 2014
Posts: 2
Received 0 Votes on 0 Posts
No heat, Trane xe 80, already ruled things out, very confused, please help!!

So my heat is out on my TRANE XE 80 TUD080C948J1. I get 3 flashes from the LED. There is a call for heat from the thermostat. The inducer motor turns on and it spins smoothly when I turn it by hand. I replaced the pressure switch, ignitor and flame sensor. One time I saw the new ignitor light up, but only once. I don't have anything blocking the exhaust and I checked the rubber tube runnng from the pressure switch to the inducer. there are no clogs there. All this and I still get 3 flashes and no heat. what am I missing? bad board? Gas valve? Any thoughts? thank you.
 
Sponsored Links
  #2  
Old 11-04-14, 08:58 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,727
Received 0 Votes on 0 Posts
Welcome to the forums!! Did you check the port where the pressure hose connects to the inducer motor? Often times the small hole will get clogged with crud and prevent adequate vacuum from closing the pressure switch. You can use an opened paper clip or small drill bit to ream it out. Make sure it is clear all the way through.
 
  #3  
Old 11-04-14, 09:31 AM
Member
Thread Starter
Join Date: Nov 2014
Posts: 2
Received 0 Votes on 0 Posts
Yep, already checked it. It's clear.
 
  #4  
Old 11-04-14, 11:07 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,727
Received 0 Votes on 0 Posts
A 3 flash code points to three things: A pressure switch problem, a vent problem or an inducer problem. You checked the vent, replaced the pressure switch, and stated the inducer port and hose is clear. The fact that you replaced the ignitor but has only glowed once would indicate either the pressure switch is not closing, the control board is not sending 115V to the ignitor or the inducer motor is not creating enough vacuum to close the pressure switch.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: