Furnace works fine with heat but shuts off after few minutes


  #41  
Old 11-19-14, 06:13 AM
E
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
After removing one connector

Placed jumper between two switch terminal and got flashing error on control board - pressure switch open with induce on

Then


Placed jumper between WIRES and system ran without any issue
 
  #42  
Old 11-19-14, 06:29 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
I suggest you restore pressure switch wires to original configuration. If the furnace ignites and operates for awhile use your finger to flick the pressure switch to see if the pressure switch opens. That would indicate weak contacts.
 
  #43  
Old 11-19-14, 07:11 AM
E
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, will try when i get home later today. Beside what you think if it's not pressure switch then is it inducer?
 
  #44  
Old 11-19-14, 08:12 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
Beside what you think if it's not pressure switch then is it inducer?
Jumping out the pressure switch merely simulates a closed pressure switch. The closing of the pressure switch is meant to be accomplished by the inducer when the vent system is in proper working order. The only accurate way to prove if the pressure switch is defective is with the use of a magnehelic gauge or manometer.

To verify the operation of the pressure switch during a call for heat the magnehelic gauge or manometer is connected into the pressure switch tubing with tees so that you are reading the negative pressure developed by the inducer. This is what the pressure switch is sensing and closes by. Pressure switches labels have their close setting shown on the label. With the inducer running, the gauge or manometer will indicate the pressure sensed by the pressure switch. This pressure should be higher than the close setting indicated on the label. If the pressure is not above the switch setting, there is a problem with the furnace. If the gauge or manometer indicates higher pressure than the pressure switch close setting indicated on the label, yet the switch does not close, the pressure switch is defective.

Some of the causes of an open pressure switch during a call for heat are debris in the inducer blower housing, seized induced draft blower wheel, failed inducer motor, cracked heat exchanger, pressure switch stuck open, etc.

So without a gauge or manometer about all you could do is replace the pressure switch and see if it corrects the issue you are having.
 
  #45  
Old 11-19-14, 10:51 AM
E
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
I searched few manometers and looks like there are different types, do you have any recommendation?
 
  #46  
Old 11-19-14, 02:23 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
You need one which will read down to 0.1" W.C. It must also be able to read negative pressure.
 
  #47  
Old 11-19-14, 04:02 PM
E
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
So i did finger flicking on pressure switch while it was closed and heat ON... it did not open to stop the system.

So does that mean its not weak contact and may not be bad then.? May be its something inducer portion you mentioned.. huh.. next big phase now
 
  #48  
Old 11-19-14, 04:44 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
So i did finger flicking on pressure switch while it was closed and heat ON... it did not open to stop the system.
How long were you able to get the furnace to operate? It doesn't prove anything really. I always flick them and if they shut off that easily I replace them because the contacts are probably getting weak. The manometer tells the whole story whether or not the inducer is doing it's job and if the pressure switch is not doing it's job if the correct pressure is being supplied.

Did you perform the test to check voltage across the pressure switch to see if it will remain at 0V while the inducer is running?
 
  #49  
Old 11-21-14, 04:45 PM
E
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
Update.. i came home y'day and temperature was down to 65 and furnace wasn't running.... so not sure what was going through.. but i gave hard flick to pressure switch and guess watch.. since then furnace is working 100% fine.

i think there must be something wrong with pressure switch.. i guess will order new one to replace.

its been about 24 hours and 20 degress outside.. and furnace is keeping it up..
 
  #50  
Old 11-21-14, 05:11 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Yup, sounds like it's pressure switch time.
 
  #51  
Old 11-21-14, 05:41 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,374
Upvotes: 0
Received 2 Upvotes on 2 Posts
Glad to you hear you were able to narrow down the culprit of your issue. Here is a link to a parts diagram and list (page 10 and 11) for your furnace:

http://www.nordyne.com/literature/7087000.pdf

It is important to match the specs of the pressure switch.
 

Last edited by firedawgsatx; 11-21-14 at 06:05 PM. Reason: Added link
  #52  
Old 11-21-14, 06:04 PM
E
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks everyone for your help.. especially @firedawgsatx
 
  #53  
Old 11-22-14, 12:25 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
Ummmm. This thread seems to illustrate ther weaknesses of GUESSING AND SUPPOSING as diagnostic methods.


 
  #54  
Old 11-24-14, 04:29 AM
E
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
I understand your skepticism however i put in exactly what happened... May be THIS PART was made by 20th century boy

I just got new pressure switch and looking to buy manometer, let me know if any expert recommendation.
 
  #55  
Old 11-24-14, 04:19 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
I use & have had good luck with the 2 port version of this manometer. No idea as to cost. EM151 | UEi Test Measurement Tools
 
 